Leaky well pipe (PICS attached)

Users who are viewing this thread

Messages
132
Reaction score
0
Points
16
Location
Connecticut
I have a small leak in the wall where the water supply pipe from the well enters the house. To be clear, it's a groundwater leak....not the black well pipe.
It only leaks when there is significant rainfall, but it is annoying nonetheless.

I tried to fix the leak by packing the area with some of that DryLok Masonry crack filler (comes in a caulk tube) but that didn't work.

So, what is the best solution?
Is this a DIY job?

thanks.
mm
 

Attachments

  • Pipe 1.JPG
    Pipe 1.JPG
    37.7 KB · Views: 555
  • Pipe 2.jpg
    Pipe 2.jpg
    27.5 KB · Views: 574
  • Pipe 3.jpg
    Pipe 3.jpg
    16.1 KB · Views: 555

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
leak

WHOA! it those wires are actually cemented into the wall, then the chances that ANYTHING that was packed into the wall to seal the hole actually completely filled it are very SMALL. WHO would run plain wires like that? You can try hydraulic cement, which is a powder.
 
Messages
132
Reaction score
0
Points
16
Location
Connecticut
WHOA! it those wires are actually cemented into the wall, then the chances that ANYTHING that was packed into the wall to seal the hole actually completely filled it are very SMALL. WHO would run plain wires like that? You can try hydraulic cement, which is a powder.

by your post, i guess this wasn't done properly...

Who should I call to make it right? A plumber, electrician?
I assume it is the well company who ran the pipe and the wires, when the house was built and the well was dug......should I call them to make it right? (House and well are about 16 years old).

And, what is the "right way"? Should the wires be in some sort of conduit?

thanks.
mm
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
That type of installation is the norm on the east coast. It has been used for many decades. Usually there is no problem with water leaks or the wires/cable or water line(s).

To fix your water leak problem you will probably have to go outside the wall and either plug the hole and get the wires and water line flat to running downhill away from the wall and/or, cover the wires and line with plastic out from the wall a couple feet to shed water coming down from rain gutters or a roof without any gutters. Or add dirt along the side of the house above this area so it slopes away from the wall a couple feet. Or add roof rain gutters, or fix existing overflowing rain gutters above this area.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Well that makes two in a row that need to be moved to the electrical forum. I'm pretty sure that violates a whole bunch of codes. OK, I know that violates a bunch of NEC codes relating to proper protection etc.
 

Rich B

DIY Senior Member
Messages
285
Reaction score
1
Points
16
Location
New Jersey
I have a similar deep well setup. No leaks thru the wall and the hole was sealed with cement. The pumps electrical wiring is in a seperate plastic pipe and goes thru the wall and to the pump controller. My well was installed by one company and I ran the 220 volt electrical feed for them from my panel. If you wanted the wiring covered as it should be an electrician could easily disconnect the wires from the pump controller and feed them thru some plastic seal tight or other shielding and reconnect them at the controller. The thru the wall area of the wires is not easy to fix. You'd need to dig them out and then what about outside in the trench to the pump? I would use some fast drying cement to try and seal the leak but the exposed wiring makes it tough to work around them. The wiring was definately poorly done by the installer.
 

Rich B

DIY Senior Member
Messages
285
Reaction score
1
Points
16
Location
New Jersey
Gary...I am not an electrician but did work as one right out of high school many years ago. I do work in a related field today. I don't believe wires are allowed to be exposed like that without a covering. Direct burial to me means UF service type cable or those wires inside grey PVC for protection. Individual wires should be covered with an outer jacket or run inside a pipe. I work in the standby generator field. NO wires are allowed to be run in such a manner in any building I have even been in. I live in the northeast and have a typical deepwell installed in 1988. No inspection was ever done as I recall but there's no way I would have accepted wiring looking like that. I was present when that well was dug and connected and installed. My Code Check guide states that direct burial UF type cable needs to be protected as it enters and exits a buidling and they are talking about jacketed type cable.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Let's get HJ to bump the thread over to the electrical forum and see what those licensed boys have to say. I could look it up in the NEC book but damn that's a big book and reading it makes my head ache :D

If it was installed before the town or city adopted the electrical code then I would guess that it is indeed grandfathered. Still, kids, dogs weed wackers all could do a number on it.
 

Doherty Plumbing

Journeyman & Gas Fitter
Messages
810
Reaction score
5
Points
0
Location
Penticton, BC
Website
www.facebook.com
I have a small leak in the wall where the water supply pipe from the well enters the house. To be clear, it's a groundwater leak....not the black well pipe.
It only leaks when there is significant rainfall, but it is annoying nonetheless.

I tried to fix the leak by packing the area with some of that DryLok Masonry crack filler (comes in a caulk tube) but that didn't work.

So, what is the best solution?
Is this a DIY job?

thanks.
mm

To answer the question I would use roofing patch tar (you can buy it in small quanities). I use it all the time to seal up foundation walls when we run new water mains through the foundation. It works great.
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
Gary...I am not an electrician but did work as one right out of high school many years ago. I do work in a related field today. I don't believe wires are allowed to be exposed like that without a covering. Direct burial to me means UF service type cable or those wires inside grey PVC for protection. Individual wires should be covered with an outer jacket or run inside a pipe. I work in the standby generator field. NO wires are allowed to be run in such a manner in any building I have even been in. I live in the northeast and have a typical deepwell installed in 1988. No inspection was ever done as I recall but there's no way I would have accepted wiring looking like that. I was present when that well was dug and connected and installed. My Code Check guide states that direct burial UF type cable needs to be protected as it enters and exits a buidling and they are talking about jacketed type cable.
Well Rich, I know you're right, the electrical code will call for conduit.

My point is that there are probably a million plus wells (that is literally and I have personally seen thousands of them in PA and in pictures from across the US where there is no conduit) installed that way and weed wackers are kept away from the wires or at least not started in the basement next to the pressure tank; or the guy cuts his wires and suffers from his dumb ass carelessness, and should learn something from that screw up but I doubt it would be to redo his wiring inside conduit.

Tell me, the next one installed like that that has a problem will be the first you ever heard of having a problem right? I'm 67 next month and I've been around wells since 1965, I can not remember any problem with wiring done that way and some were even done with Romex!! instead of pump cable.

Peter, you leave the Sparkies alone, they are already stressed enough.

Doherty, petroleum based products and PE pipe water lines should never come in contact with each other; it's a real no no getting them together. They can damage the PE (and other plastics) and can contaminate water in the line.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Well Rich, I know you're right, the electrical code will call for conduit.

My point is that there are probably a million plus wells (that is literally and I have personally seen thousands of them in PA and in pictures from across the US where there is no conduit) installed that way and weed wackers are kept away from the wires or at least not started in the basement next to the pressure tank; or the guy cuts his wires and suffers from his dumb ass carelessness, and should learn something from that screw up but I doubt it would be to redo his wiring inside conduit.

Tell me, the next one installed like that that has a problem will be the first you ever heard of having a problem right? I'm 67 next month and I've been around wells since 1965, I can not remember any problem with wiring done that way and some were even done with Romex!! instead of pump cable.

Peter, you leave the Sparkies alone, they are already stressed enough.

Doherty, petroleum based products and PE pipe water lines should never come in contact with each other; it's a real no no getting them together. They can damage the PE (and other plastics) and can contaminate water in the line.

So the gist of all this is that in your opinion the wiring is ok?
 

Rich B

DIY Senior Member
Messages
285
Reaction score
1
Points
16
Location
New Jersey
Exposed wiring is a NO-NO.....period! If I'm a home inspector and I see that I am writing it up as a must fix. If I am an electrical inspector I am definately flagging that.

How about a dog that likes to chew things or a kid playing in the basement and he finds something sharp to jab at those wires and the pump is running! Not a good scenario. Electrical safety is just common sense and should be taken seriously. Exposed wiring is a hazard and not acceptable to me. I can take a picture of mine if you'd like to see it.....NO exposed wiring....
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
Exposed wiring is a NO-NO.....period! If I'm a home inspector and I see that I am writing it up as a must fix. If I am an electrical inspector I am definately flagging that.

How about a dog that likes to chew things or a kid playing in the basement and he finds something sharp to jab at those wires and the pump is running! Not a good scenario. Electrical safety is just common sense and should be taken seriously. Exposed wiring is a hazard and not acceptable to me. I can take a picture of mine if you'd like to see it.....NO exposed wiring....
I'm not buying that you run all your exposed computer, lamp, TV. radio etc. etc. etc. power cords in your house in conduit. Or that you would if you have kids and dogs.

And more than likely until that line is replaced it is probably grandfathered.
 

Doherty Plumbing

Journeyman & Gas Fitter
Messages
810
Reaction score
5
Points
0
Location
Penticton, BC
Website
www.facebook.com
Doherty, petroleum based products and PE pipe water lines should never come in contact with each other; it's a real no no getting them together. They can damage the PE (and other plastics) and can contaminate water in the line.

Ah didn't know that! We don't use PE piping much (I don't install pump/well systems).
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Gary is right about the east coast...almost all the ones I work on look similar to this...all grandfathered in...it just the way it was done....
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
That they were done that way does not make it right though. And the NEC has been around for a long time indeed. They were done that way because many states didn't and still don't license and regulate pump installers so no permit was ever pulled and the work was never inspected.
The same thing goes for filters that were installed and drained into unvented traps that the installer cut into the main drain lines. There was and is a lot of this monkey business going on because nobody inspects the work so the installer is not held accountable until something goes wrong.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Yes, but now we all know better; right?[/QUOTE]

I hope that we do. giving folks the impression that letting things that are not to code, dangerous or both is ok would set a very bad precedent indeed. We are, after all, here to help people to do things right. If that was my property I would have disconnected the wires and re-installed them in PVC conduit by now before someone gets hurt and sues me. And I'll bet those same wires run unprotected inside the basement.
 