Gonna need pictures and or a better description on this but generally the expansion tank is mounted on an air elimination device (I like spirovent) and the fill valve should be mounted at the same point because this is the point of no pressure differential in the system. The main circulator should be mounted just downstream of the tank and fill valve. 837' of pipe. How big is the pipe? either way a little Taco 007 or a Grundfos cartridge pump is not going to cut it for that distance, You can get pipe friction loss and pump performance curves from www.taco-hvac.com