I replaced a ceiling light fixture that takes a j-type halogen bulb, and the wires seemed to be "baked" from the heat given off by the bulb. Part of each wire broke off when I removed the wire nuts, and the insulation on the remaining wires was so hard, I had to "chip" it off rather than "strip" it off to make the new connections.

I replaced the fixture with a conventional light fixture that uses CFL's. My parents have about 4 more of these j-type bulb fixtures. I advised them to go ahead and replace these fixtures, as well. Has anyone else ever heard of wires "baking" from the heat with this type of fixture?
 

Sixlashes

Plumber in Previous Life
Messages
82
Reaction score
0
Points
0
Location
Pensacola. FL
How old is the house? It may have 60 degree C (centigrade) rated wiring. I'll bet those (newer) fixtures require at least 75 degree C rated wires in the installation instructions. If this is the case, it seems the wires simply got too hot for the insulation. It is possible to splice newer (90 degree C rated) wire in the system, but that would most likely be a job for an electrician.

If the wiring is new already, the fixture is getting too hot. Is the fixture installed per the manufacturer's instructions? There is something wrong causing too much heat. Have the light(s) cut off unexpectedly for no apparent reason? If not, is also possible the temperature limit switches are defective and the fixture is overheating without tripping them.

Either way, I would not use the fixtures in their present configuration for obvious reasons.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
Yes I have seen quite a bit of this in older homes. Also with wall mounted fixtures like in a bathroom.

And that is the reason fixtures will say 60 watt bulb max or whatever. Lots of heat generated and all going straight up.

Also the reason they say not to place insulation in the attic over ceiling light fixtures - let the heat out.

Important to follow installation instructions as to the wire type as pointed out above as well as insulation above fixture, wattage of bulb(s), and other things.

Basically follow the installation instructions when installing the new fixtures and replace the old damaged wiring.
 

Kiko

Member
Messages
186
Reaction score
0
Points
16
Location
Royal Oak, Michigan
Thanks to you both.

An electrician installed all new wiring in this house when my parents bought it 15 years ago, and these halogen fixtures were installed then. I believe the heat given off from these j-type bulbs is what baked the new wiring from the outside, rather than from the inside due to 60 C rated wiring.

I was just wondering if anyone else has had this experience with j-type fixtures.
 