  1. #1

    Default bonding/grounding and pex

    I have been reading some of the posts about grounding after installing pex. If an existing galvanized system were grounded to the cold water main where it enters the house couldn't the old galvanized conceivably remain grounded via a jumper? If the old galvanized system were left in place and a new pex system installed around it couldn't a jumper wire serve to connect the remaining galvanized system back to the cold water main keeping the original ground intact?

  2. #2
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    I think you're mixing up some terminology here.

    Article 100 of the NEC defines grounding as, "Establishing a connection, whether intentional or accidental, between an electrical circuit or equipment and the earth or to some conducting body that serves in place of the earth." Grounding provides a path for conducting electrical energy to earth to prevent arcing, heating, or explosion during a lightning strike.

    The NEC defines bonding as, "The permanent joining of metallic parts to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed." As it relates to a communications system, the primary purpose of bonding is to equalize ground potential of, and eliminate static discharge between, equipment. If a potential difference exists between two objects connected by a conductor, electrons will flow along the conductor from the negatively charged object to the positively charged object, damaging electronics in its path. The flow of electrons happens until the two charged objects are equalized and the potential difference no longer exists.

    Other than that, I can't really be sure what you are asking.

    You say, "if an existing galvanized system were grounded to the cold water main where it enters the house couldn't the old galvanized conceivably remain grounded via a jumper?" For one, I think you mean bonded. Second, I don't know how the "old galvanized" and the "cold water main" differ.

    The NEC requires the cold water main, as you call it, to be bonded within 5' of the entrance into the building. If it's not metallic, no bonding. After that point if it transitions back to metallic, I don't think that isolated portion needs to be bonded.


    Jason

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default grounding

    If it is not metallic, our electrical panel boxes have to be labeled "Non metallic water service pipe" and a substitute ground path/method used in place to the plumbing system.

  4. #4

    Default bonding/grounding and pex

    Let's say that one foot of galvanized pipe in a galvanized plumbing system is removed. The previous system was bonded through the water service entrance. Once that one foot of galvanized pipe is removed the system is no longer bonded. Isn't the solution as simple as running a jumper to bridge the gap where the galvanized sections are now separated?

  5. #5
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    It must be bonded with 5' of the entrance into the building per the NEC. If you remove that said one foot section before it is bonded, then yes you would need a jumper. If that said one foot section is after it's bonded (over 5' from the enterance), the no jumper needed.

  6. #6

    Default

    Thanks. I have filed you away for my future engineering questions for you may have noticed that I am not one.

  7. #7
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Quote Originally Posted by hj View Post
    If it is not metallic, our electrical panel boxes have to be labeled "Non metallic water service pipe" and a substitute ground path/method used in place to the plumbing system.
    Why would that need to be labeled? Local code?