capacitor burn out

Users who are viewing this thread

dragnuts

New Member
Messages
5
Reaction score
0
Points
0
Location
australia
have just put in new bore pump (grundfos 1.5kw) and new control box. Ran for 20 minutes then noticed fluid dripping out of control box.one of the 2 capacitors was hot so i stopped pump but will not start again so i replaced the capacitor and it done the same thing.What would cause this?
 

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
have just put in new bore pump (grundfos 1.5kw) and new control box. Ran for 20 minutes then noticed fluid dripping out of control box.one of the 2 capacitors was hot so i stopped pump but will not start again so i replaced the capacitor and it done the same thing.What would cause this?

If the pump is brand new and the control box is brand new, then most likely you have something wired incorrectly.

Rather than trying to fix brand-new equipment, I would have contacted the manufacturer(s) immediately if equipment self-destructed when energized.

Can you tell us how it's wired?
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
It is common with electronics for one thing to be bad and cause another component to fail.

If alternating current gets through to an electrolytic capacitor, the capacitor will fail for example. The circuit should only allow DC to get through to these types of capacitors.

I would send it back. They are going to need factory schematics and an oscilloscope to "see" what is going on with the circuit.
 