Cellulose at a foot deep is 1.5-2lbs/ square foot- if the garage is roughly 22x22 you're lookin' at close to a half ton of dead-weight loading for just the insulation alone, added to a comparable amount for the OSB. It's not nuthin'.
It's ~30% more surface area, and would have to be done with batts (or $pray foam) and a ventilation gap to the roof deck is required, but going cathedral-ceiling style and king-pinning the tie-spans to handle the increase in roof load would be easier. If you wanted more R at mininum weight, sheathing the rafters with iso (pick your thickness, figure R6.5/inch) will have the least loading factor. Use thermal-rated foil faced iso to avoid having to add a layer of gypsum or wood sheathing for a thermal barrier (fire code stuff.)