    Good Morning,

    I am trying to run an outdoor lighting system from my main panel to the front gate of my property. The total one-way run to a 3-way switch at the gate will be 275 feet so I guess that the total circuit length will be 550 feet plus a few feet to the lights. The load will be approximately 660 watts (5.5 amps?) of outdoor spot lights and be connected to a 15-amp breaker at the main panel. Can I run from the main panel to the LB fitting with 12-2 NM-B and then run from the LB fitting with 10 gauge to a junction box approximately half way to the 3-way switch at the gate? Id like to come from the junction box to the 3-way switch at the gate with 12 gauge as I have the appropriate lengths of the different gauges of wire already.

    Thanks in Advance!
    SR

  2. #2

    Default

    When you run wire long distances, you get "voltage drop". There are many free "calculators" for this on the internet. Search google.com for the words...

    voltage drop calculator

    Some are easier to use than others. (You would select 1 phase or single phase.)

  3. #3
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    You can splice inside the lb, but it must have enough room to handle the connductors.
    It will be better to install a weather proof box and make the splices there.

    Do you not have enough wire to make a complete run without splicing in the middle?
    Yes I am A Pirate-Jimmy Buffett

  4. #4
    DIY Member Ford2001's Avatar
    Join Date
    Sep 2009
    Location
    Manchester, Vermont
    Posts
    32

    Default

    Trying using UF-B 103/ground cable.

  5. #5

    Default

    1. Use a jbox instaed of an LB

    2. I always suggest against using birect buried cable/wire. Conduit is cheap insurance from damage, Stuff happens.

    3. Your voltage drop on 275' of #12 is about 5% or 6 volts. I would use #10 for that distance.

  6. #6
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Incands will last longer at lower voltages.

  7. #7
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    A lot longer.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default wire

    IF you are going from the panel, to the first switch, to the second switch, and then to the lights, you will need THREE wires, and the distance will only be 275'. If you go from the panel to the "second" three way, and from there back to the first one, and also to the lights, then you need FOUR wires and the distance will be 550'. PLus, either one will also need a ground wire.

  9. #9
    DIY Senior Member Runs with bison's Avatar
    Join Date
    Aug 2009
    Location
    Midwest
    Posts
    892

    Default

    I would hope that much light will only be on infrequently. It would be awfully wasteful/hard on the wallet to have it on dusk to dawn (several thousand kwh/year). If it's going to be on dusk to dawn then you might want to consider more efficient lighting solutions.