Are you sure you're even allowed to place the plumbing inside the footing like that? Where I am from this certainly wouldn't be allowed.
|
|
|
-Slab-on-grade floor
-toilet backs up to an exterior wall
My vent stack/end-of-line clean-out will come up through the footing/slab. In a typical above-grade install, the closet bend would point back to the wall and T into the stack, like this-
But how do I accomdate the requirement for a 2"-oversize sleeve in the footing penetration, if I've got a fitting buried in the footing? Is this a case where a horizontal vent is permitted due to structural/grade restrictions? like this-
![]()
Are you sure you're even allowed to place the plumbing inside the footing like that? Where I am from this certainly wouldn't be allowed.
You first picture is correct !
You just put a 3" x 2" reducer bushing into the top of your clean out tee and
extend the 2" vent up from there, also you get foam wrap and make 3 or 4
turns around the abs pipe and fittings where ever they are buried or cross
though the concrete footing and slab !
This gives room for the abs and concrete to slide without breaking the abs
like in thermal expansion of the abs when you run hot water though it !
This go's for all abs concrete penetrations
MACPLUMB 777
E-MAIL JERRYMAC@TROJANWORLDWIDE.COM
35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER AND BOILERS SINCE JAN, 1989
281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
That's what I'm familiar with. But new code (not sure if it's UPC or California bldg code - which is a mix of UPC and our own mod's due to the seisimic zones here), is calling for all footing penetrations to be sleeved in pipe 2" larger than the diameter of the line you're running.
Guess I'll be visiting the bld'g dept tomorrow to find out how they want it.
Put your Y BETWEEN the elbow and the toilet and run the vent back to and up inside the wall.
Latest California Building Code requires all footing penetrations to be sleeved in 2-sizes larrger pipe. But apparently many (most?) local AHJ's aren't enforcing it, because it's not practical in situations like mine, where there's a tub, shower or W.C. along an exterior wall.
So it's standard layout and wrap in foam. I did drop the combi to the bottom of the stack -- I'm thinking the 18" free-fall from the toilet horn should make for a very effective flush![]()
Thanks, all, for your help.