Thread: Installed 240v Dryer, used 10 gauge wire, 20 amp breaker-breakers flicking off

  1. #1
    DIY Member 87vertgt's Avatar
    Join Date
    Sep 2009
    Location
    Chicago,IL
    Posts
    52

    Question Installed 240v Dryer, used 10 gauge wire, 20 amp breaker-breakers flicking off

    What did we do wrong? also the breaker gets warm too...


    thanx gents

  2. #2
    DIY Member 87vertgt's Avatar
    Join Date
    Sep 2009
    Location
    Chicago,IL
    Posts
    52

    Default

    correction used a 30 amp double breaker

  3. #3
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Well, saying the breaker "keeps flicking off" is not much of a description.
    How long before it trips?
    Is the dryer new or old?
    Did you wire it right?

    You say it gets warm. Like hot? Or warm that you can keep your hand on it?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    If the run to the dryer is excessively long, you might want to upsize the wire, too. Probably not an issue. If you have a multimeter, you could check the voltage at the panel, then again at the dryer with it running. Don't do this if you aren't comfortable and knowledgable about working on power. If there is a significant voltage drop, then you have a bad connection somewhere or the wire is undersized (shouldn't be, though). Could be in the plug, or cord, or maybe even at the panel. Does the breaker get warm, too? Could have a bus bar problem or a bad breaker.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    DIY Member 87vertgt's Avatar
    Join Date
    Sep 2009
    Location
    Chicago,IL
    Posts
    52

    Default

    thanx for the response gents


    when I say "flicking off" i mean the breaker is turning off.

    The dryer is new.

    I didnt wire it. I electrian did.

    The breaker gets warm, not hot.

    The cord is new. The wire is new. I am gonna replace the new breaker with another new one.

    Whats a Bus bar?

  6. #6
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    Call the electrician back.

    I hope the electrician wired the receptacle properly. If the neutral and one of the hots is reversed, you could be running 240 volts to parts that are 120 volt rated.

    As an aside, I also hope he remembered to remove the grounding jumper in the dryer if this is a new four-wire set up.

    Call the electrician back.

    If he made both of these mistakes, fire him.
    Last edited by Ian Gills; 10-16-2009 at 02:13 PM.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default dryer

    IF he connected a hot lead to the neutral terminal, AND did not remove the jumper, the customer will probably FRY before the electician is FYRed (sic).

  8. #8
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    Or with a four wire set up, it would trip the breaker.

    Absolutely anything could be wrong with it. Call the electrician back.

    Only the English should play with 240 volts.

    While inventors in many countries contributed to electric power technology, the U.S. was way out front in putting that technology to practical use. In the early days, lower voltages were the most practical for electric lights-- higher voltages burned out the bulbs. So the hundreds of power plants built in the U.S. prior to 1900 adopted 110 volts (or 115 or 120 volts) as their de facto standard.

    Trouble was, power transmission at higher voltages was more efficient-- and you didn't have to use so much copper in the wires. By the time most European countries got around to making big time investments in electricity, the engineers had figured out how to make 220-volt bulbs that wouldn't burn out so fast. So, starting in Germany around the turn of the century, they adopted the 220-volt (or 230- or 240-volt) standard. But the U.S. stayed with 110 volts (today it's officially 120 volts) because it had such a big installed base of 110-volt equipment.
    Last edited by Ian Gills; 10-16-2009 at 02:50 PM.

  9. #9
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by Ian Gills View Post
    Call the electrician back.
    The ONLY answer.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  10. #10
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    Quote Originally Posted by Ian Gills View Post
    Only the English should play with 240 volts.
    What about the Italians & Germans & French & all those other folks?
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...
    __________________
    Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.

  11. #11
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    What is the brand of the main pannel?

    It doesn't happen to be Federal Pacific does it?

    Call the electrician back...

  12. #12
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    Quote Originally Posted by Ian Gills View Post
    Only the English should play with 240 volts.
    You shall not disconnect my hot tub from 240v !!
    Nor my HW heater, dryer, stove, AC, radiant floor heat.........
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  13. #13
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default ian

    quote; Trouble was, power transmission at higher voltages was more efficient-- and you didn't have to use so much copper in the wires.


    You did not mention that at the higher voltages electromagnetic forces on the center of large conductors becomes a detriment, so "hollow" wires are more efficient.