Commercial venting

Users who are viewing this thread

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
11 story building.

Over 80 wall hung toilets and 30 urinals.

Where would the vent be and how big would it be?

Would I find a 4 inch piece of PVC sticking out of the roof if I ventured up there?

If it's any bigger, what would stop people falling in? :eek:
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
You would probably find two 4's.

Anyone who gets up on the roof of an 11 story building either knows how to look out for himself, or deserves to fall in!
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Dwv

The number of stories and/or the number of fixtures by themselves mean nothing. HOW the fixtures are arranged on the various floors determines the pipe sizes and their arrangement. You will NOT find a 4" PVC sticking out of the roof, because VERY FEW, if any, codes allow ANY plastic piping over three stories. The fact that very few people would fit into a pipe smaller than 12" is what keeps them from falling in.
 

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
11 Stories would likely be a Solvent system.
(2) 4's or maybe 6's (although unlikely) depending on how they designed it and if they were accounting for future uses.
You may also find a few 3's if they have typical fixture locations away from the main plumbing stack(s).

Sovent design manual
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
Wow. I'm gonna go DIY commercial style.

Why doesn't the hot water take ages to come up to the 9th floor, if I am the first one to wash my hands in the morning? I sure get hot water quicker than in my single story rambler at home?
 
Last edited:

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
You might have a heater close (mechanical closet nearby?) or the whole building has a recirc system.
 

loafer

Mechanical Engineer
Messages
50
Reaction score
0
Points
6
Location
Maine
Wow. I'm gonna go DIY commercial style.

Why doesn't the hot water take ages to come up to the 9th floor, if I am the first one to wash my hands in the morning? I sure get hot water quicker than in my single story rambler at home?

In large hotels the hot water is constantly circulated through a loop, similar to a force hot water heating system. Branches from the circulating loop supply each room which results in virtually instant hot water. Other large buildings may use similar techniques.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
piping

SoVent is a very UNCOMMON system, therefore, an 11 story building would not necessarily have one. There are many ways to supply water to the various floors. A pump in the basement with PRV's at each floor, or a few PRV's each serving several floors, a tank on the roof downfeeding the water system, or a hybrid with the pump feeding the lower floors and the tank taking care of the upper ones. And, these are just a few of the many possible combinations.
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
Fascinating. Is it the same sort of issue for all buildings three-stories and over or are there other cut-offs?

For example, above 50 stories do new things come into play with plumbing?
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
One of the local hotels here uses the Sovent system.
Staying there, I noticed the trap making noise like it was being siphoned.
A lot a noises coming from it.
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
My work would not let me on to the roof to have a look. The guard asked if I was going to jump or fly?

If I had a helicopter they could make special arrangements.

So I guess DIY, commerical-high rise style is a no no.

That's a shame.

Let's all DIY high in the sky!
 
Last edited:

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
high rise

Height creates to problems. Water lines develop higher pressure, and drain lines develop excessive velocity. Both situations require special features to minimize their effects. WHAT is done may be unique to each building because there are many ways to ameliorate the effects of height. Imagine the pressure to get water to the top of the Burg Dubai 2900 foot high building, or the terminal velocity of water draining from a top floor toilet.
 