Thread: "Potential Starting Relay"

  1. #1

    Default "Potential Starting Relay"

    Hello All. Can Anyone Cross referance my Well Control Box Potential Starting Relay, to a 50 amp points rating, verses my 35 amp one? I Now have an "ELECTRICA" PN#
    RVA 2AL KL Starting relay for my 3hp pump. I want a Starting relay with the same specs/ PU-224-252, and DO-40-105, (or close to it. Except I want one with a 50 amp points rating), verses my 35 amp rating, that I now have. Also the better the material the points are made out of would be nice!!!! Any Brand will do! Any Ideas, or part numbers would be appreciated!

    Thanks,

    lzenglish
    Last edited by lzenglish; 09-26-2009 at 01:54 AM.

  2. #2
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Why? Upsizing the relay could lead to frying the pump motor.

  3. #3

    Default

    Why? That is a long story, lets just say because I want too! Now I assure you I have not, and would never, Jumper my thermal overload switch (that protects the pump from frying), or increase my circut breaker amp size (which also protects the pump from frying). If you have an (Air Maker System), with an (AVC), and snifter valve etc., you would know that it is inevitable the AVC will go bad, or the tank will water log at least every now and then. When it does it short cycles, when it short cycles, the starting relay points (Pit), until the themal overload can trip. Once this happens, the points are never the same on a cheapo Relay. As long as the pick-up, and drop-out votages are the same, it does not matter how big I go on the size, and quality of the points.

  4. #4
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    In that case then I would head on over to grainger supplies web site. they probably have what you need.

  5. #5

    Default

    Hello again, and thanks for your replies! As far a Grainger goes, I have had an account with them since 1975, and they are good people, but do not have the technical knowlege that I need, (And do not list the relay I'm seeking). This is the reason I have posted this thread. If I get no (cross referance responses), I will start calling the manufactures, on Monday. Just thought I would try to save a few bucks on phone calls!

    Wayne

    Senior Stationary Engineer(retired)
    Last edited by lzenglish; 09-26-2009 at 01:31 PM.

  6. #6
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    How about Siemans ?

  7. #7

    Default

    Thanks, I will put them on my list to call!

    Take care,

    Wayne

  8. #8
    DIY Senior Member Bob999's Avatar
    Join Date
    Jul 2009
    Location
    Pennsylvania
    Posts
    448

    Default

    GE apparently makes one with 50 amp contacts.

    Here is a link to literature:
    http://www.geindustrial.com/publibra...TION%7Cgeneric

  9. #9

    Default

    Thanks for the Link !

    Wayne

  10. #10
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    30 mV or less across closed relay contacts at rated current = good contacts. More than 100 mV, bad.

    http://www.google.com/search?hl=en&s...&aq=f&oq=&aqi=
    Last edited by Thatguy; 09-26-2009 at 06:11 PM.

  11. #11
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Quote Originally Posted by lzenglish View Post
    Why? That is a long story, lets just say because I want too! Now I assure you I have not, and would never, Jumper my thermal overload switch (that protects the pump from frying), or increase my circut breaker amp size (which also protects the pump from frying). If you have an (Air Maker System), with an (AVC), and snifter valve etc., you would know that it is inevitable the AVC will go bad, or the tank will water log at least every now and then. When it does it short cycles, when it short cycles, the starting relay points (Pit), until the themal overload can trip. Once this happens, the points are never the same on a cheapo Relay. As long as the pick-up, and drop-out votages are the same, it does not matter how big I go on the size, and quality of the points.
    The AVC only lets out excess air. If the tank gets water logged, it is because the above ground check valve, schrader valve, or the bleeder orifice in the well is not working properly. Larger contacts will help a little but, nothing can survive the electrical arcing that happens when the switch pops open and closed from a water logged tank. And if your switch is seeing this kind of damage, just imagine the damage to the motor. Solve the problem, not the symptom. There are devices like the Cycle Sensor that will shut the pump down before there is a problem.

    See this link;
    http://www.cyclestopvalves.com/prod_sensor_geninfo.html

  12. #12

    Default

    Thanks. I have found a relay! I understand your point, but, but I think my New Heavy Duty Relay, will give me a more Reliable system. The pump is only 5 years old, and Not a (Big Box Store) drop in. Have you ever bought a (Heavy duty Device of any Kind)? I think a 35 amp rating is too small anyway, otherwise, why would they offer a 50 amp one? I cannot bunk out at the well house, if I could, I guess I would! Now my friend, what would you suggest, with a New tank, New Commercial grade, Psi Cycling Control, New Snifter valve, New AVC, No leaks, Proper Voltage, Tight Connections etc.? I do what I think I can, without breaking the rules, (such as bypasing Saftey Devices, That I have stated ! What would You say is the underlying Probem? Move? (just kidding)

    lzenglish

    PS Yes the AVC Only lets Air Out., If it is not fowled, or plugged! I Know this very well, as I have replaced Many of them!
    Last edited by lzenglish; 09-30-2009 at 02:52 PM.

  13. #13
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    The check valve that the Schrader screws into is the most important part. I donít see where you replaced it. If this check valve doesnít close properly, none of the other parts for the air charge system will work. Just using larger contacts, (that are meant for larger horse power pumps), will only move the problem further down the line. Probably to the 5 year old pump that may not last much longer. This has always been the main problem with air charge systems, which is why they made bladder tanks, so you donít need all those little air charge parts that will fail. A device like the Cycle Sensor that looks for a rapid cycle and shuts the pump off before there is a problem would be safer for the pump and would keep the points from burning.

  14. #14

    Default

    Thanks for your reply, Yes The Control Valve was replaced one Year ago! And is a (Very Top Grade One).!

    Take Care,

    Wayne

    PS. A Well and Septic is a Beautiful Thing, as long as it Works!!!!!!!!!!
    One plus, is that I'm a retired Senior Stationay Engineer, (that was Not handed to me at birth)!, But I'm not a Well Expert, as You people are, and I need all the advise I can get, and do very much appreciate Your advice, and keep it Coming please !!!!! Sorry about my bad spelling!
    Last edited by lzenglish; 09-30-2009 at 03:44 PM.

  15. #15
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    A 3hp motor should only draw between 15 and 18 amps so a 35 amp contactor is more than ample. Arcing points is arcing points no matter what the contactor is rated at and if the arcing continues it will burn up the 50 amp in the same amount of time. V-man is correct here, there is an underlying problem that has to be solved first.