MN-B, 12-3/GRD inside 2" PVC conduit

Users who are viewing this thread

Ford2001

New Member
Messages
44
Reaction score
0
Points
0
Location
Manchester, Vermont
Thinking about using 2" PVC conduit attach to the top of circuit breaker
panel. The conduit would run up the side of the wall, (note: panel is surface
mounted), then 90 over to the center of the room, where the opposite end
would terminate inside a large j-box. Something like a 6x6x4.

Yes I know thhn individual conductors would work better. But it's money
thing. Have the romex cable left over, and just want to be sure this
nothing the NEC code that would prohibit this practice.



And how exactly do you measure the dia. of 12-3 romex?

Thanks to all who show an interest and reply.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
There are code issues about putting NM cable in conduit. The ratings of the cable are based on it being in free air. But a 12-3 would FIT inside ½" conduit! What's up with running 2" conduit in your ceiling???


What do you mean by "how do you measure the size of 12-3??""??
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
?

What are you trying to do? 2" conduit seems like overkill for a single Romex wire, and if you are running a lot of them the J-box may not be the right choice.
 

Ford2001

New Member
Messages
44
Reaction score
0
Points
0
Location
Manchester, Vermont
romex cable in a 2" PVC conduit

The 2" PVC conduct witll be a continuous run from the top of the
electrical circuit breaker panel box, to were it connects with a large
j-box, something like a 6x6x4.

The ceiling will be unfinished, open raftiers. There are no plans, at this
time to finish the ceiling.

The area in question, is in a seperate building. That is currently used
only for storage. This building never had power.

My plan, is approved, will be to run, four individual, 12-3 NM-B cable
thru the 2" conduit. This can give four, 120 volt, at 20 amps. circuits.

Also, is the old timer needs a 240 volt circuit I will be able to supply that
as well.

Thanks for your previous replies.
 
Last edited:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Well, you may have code issues with 4 nm inside conduit. You will need to find out from your inspector if that is allowed. Speedy Petey is one of our NEC experts, so hopefully he will come along and give you an expert answer.
 

Jim Port

Electrical Contractor
Messages
156
Reaction score
0
Points
0
Location
Maryland
Website
www.manta.com
Since you are planning for a junction box already just run individual THHN conductors. Much easier to work with and it leave more space in the conduit.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
The main isse is that the NM won't be connected to the panel box.

Here, it would be a non issue.
 
Top