Not sure how those with the shared neutral work in GFCI circuits...
An AFCI isn't the same thing nor will it provide the desired protection as a GFCI. The AFCI detects arcs that could cause fires and then trips. The GFCI detects leakage current that might be going through you that could kill you.
I suppose the fire could kill you too, but that's a different story.
Might be time to run two new 12/2 circuits. Feed the first outlet with a GFCI recepticle in each branch and you'll be good to go.





Reply With Quote
However, your "spare" AFCIs won't work with the shared neutral, you would have to re-wire to non-shared neutrals. Also, a "combination" AFCI refers to an AFCI that can detect both series and parallel arc faults, they do not have any features of a GFCI, so you will still need either GFCI breakers or receptacles. There are only a few two-pole shared neutral AFCIs out there, if they happen to fit your panelboard they are very expensive.