I never put water piping or ductwork directly over panels. Use some common sense and you should be fine.
|
|
|
Is there a restriction on how close the water supply lines can be to the electric service panel? Currently the water supply runs directly above the main panel and I'm doing some renovations and have to move the supply line. So when I replace the line, is there some minimum distance that I need to maintain?
I never put water piping or ductwork directly over panels. Use some common sense and you should be fine.
Matt
Semi-professional plumbing designer
Enjoying life in SW Florida
Spacing requirements have to do with possible contact with the piping while working in the panel. If the pipes are overhead there would be little reason to make contact with them.
What was the distance and what do you want it to be...
Thanks for the replies so far...
This is in the basement. The panel is against the wall and the supply is 6 inches above the top of the panel and 12 inches in front of it. I was going move it over at least one joist bay (16 inches + the original 12 inches = 28 inches in front of the panel, and still 6 inches above). I could move it an additional joist bay over if necessary.
Last edited by Zenman; 09-12-2009 at 01:56 PM. Reason: fix typos
E3305.3 Dedicated panelboard space. The space equal to the
width and depth of the panelboard and extending from the floor
to a height of 6 feet (1829 mm) above the panelboard, or to the
structural ceiling, whichever is lower, shall be dedicated to the
electrical installation. Piping, ducts, leak protection apparatus
and other equipment foreign to the electrical installation shall
not be installed in such dedicated space. The area above the dedicated
space shall be permitted to contain foreign systems, provided
that protection is installed to avoid damage to the electrical
equipment from condensation, leaks and breaks in such foreign
systems (see Figure E3305.1).
Exception: Suspended ceilings with removable panels shall
be permitted within the 6-foot (1.8 m) dedicated space
http://www.inspectpa.com/forum/forum.php
My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
Yea Jar that's it, that's it exactly![]()
OK... from that it seems that no supply lines directly above the panel are allowed. It doesn't specify a distance in front of the the panel, so I guess as long there is some separation I should be good. I was going to be at least 28 inches in front of the panel (if not more), AND above 6 feet, so I shouldn't have a problem.
Thanks!