Thread: plumbing over electric panel

  1. #1
    DIY Member Zenman's Avatar
    Join Date
    Nov 2004
    Location
    New Jersey
    Posts
    58

    Default plumbing over electric panel

    Is there a restriction on how close the water supply lines can be to the electric service panel? Currently the water supply runs directly above the main panel and I'm doing some renovations and have to move the supply line. So when I replace the line, is there some minimum distance that I need to maintain?

  2. #2
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    I never put water piping or ductwork directly over panels. Use some common sense and you should be fine.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default water

    Spacing requirements have to do with possible contact with the piping while working in the panel. If the pipes are overhead there would be little reason to make contact with them.

  4. #4
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    What was the distance and what do you want it to be...

  5. #5
    DIY Member Zenman's Avatar
    Join Date
    Nov 2004
    Location
    New Jersey
    Posts
    58

    Default

    Thanks for the replies so far...

    Quote Originally Posted by Cass View Post
    What was the distance and what do you want it to be...
    This is in the basement. The panel is against the wall and the supply is 6 inches above the top of the panel and 12 inches in front of it. I was going move it over at least one joist bay (16 inches + the original 12 inches = 28 inches in front of the panel, and still 6 inches above). I could move it an additional joist bay over if necessary.
    Last edited by Zenman; 09-12-2009 at 01:56 PM. Reason: fix typos

  6. #6

    Default

    E3305.3 Dedicated panelboard space. The space equal to the
    width and depth of the panelboard and extending from the floor
    to a height of 6 feet (1829 mm) above the panelboard, or to the
    structural ceiling, whichever is lower, shall be dedicated to the
    electrical installation. Piping, ducts, leak protection apparatus
    and other equipment foreign to the electrical installation shall
    not be installed in such dedicated space.
    The area above the dedicated
    space shall be permitted to contain foreign systems, provided
    that protection is installed to avoid damage to the electrical
    equipment from condensation, leaks and breaks in such foreign
    systems (see Figure E3305.1).
    Exception: Suspended ceilings with removable panels shall
    be permitted within the 6-foot (1.8 m) dedicated space
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  7. #7
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Yea Jar that's it, that's it exactly

  8. #8
    DIY Member Zenman's Avatar
    Join Date
    Nov 2004
    Location
    New Jersey
    Posts
    58

    Default

    Quote Originally Posted by jar546 View Post
    E3305.3 Dedicated panelboard space. The space equal to the
    width and depth of the panelboard and extending from the floor
    to a height of 6 feet (1829 mm) above the panelboard, or to the
    structural ceiling, whichever is lower, shall be dedicated to the
    electrical installation. Piping, ducts, leak protection apparatus
    and other equipment foreign to the electrical installation shall
    not be installed in such dedicated space.
    The area above the dedicated
    space shall be permitted to contain foreign systems, provided
    that protection is installed to avoid damage to the electrical
    equipment from condensation, leaks and breaks in such foreign
    systems (see Figure E3305.1).
    Exception: Suspended ceilings with removable panels shall
    be permitted within the 6-foot (1.8 m) dedicated space
    OK... from that it seems that no supply lines directly above the panel are allowed. It doesn't specify a distance in front of the the panel, so I guess as long there is some separation I should be good. I was going to be at least 28 inches in front of the panel (if not more), AND above 6 feet, so I shouldn't have a problem.

    Thanks!
    Last edited by Zenman; 09-12-2009 at 07:55 PM.

  9. #9
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by Zenman View Post
    OK... from that it seems that no supply lines directly above the panel are allowed. It doesn't specify a distance in front of the the panel, so I guess as long there is some separation I should be good. I was going to be at least 28 inches in front of the panel (if not more), AND above 6 feet, so I shouldn't have a problem.

    Thanks!
    Correct, the issue code wise is leaking *and sweating from HVAC* down onto the panel or feeders.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida