Thread: This box fail to pass inspection

  1. #1
    DIY Member Ford2001's Avatar
    Join Date
    Sep 2009
    Location
    Manchester, Vermont
    Posts
    32

    Cool This box fail to pass inspection

    Electrical inspector said that the 4"Sq. x 2-1/8 deep junction box what
    to small for the number of conductor inside it.

    Before I rip this box apart and replace it with a 4-11/16"sq. x 2-1/8 deep,
    why can't I just add 4"Sq. x 1-1/2" box exteneion ring?

    You should also know, that I plan to use a 4"Sq. box cover, 2-gang,
    raise 1".

    There is no local code in my area, all inspection are done by the State.
    The State used the NEC code 2008 editiion, with do not have a copy
    of at this time.

    Thanks

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by Ford2001 View Post
    why can't I just add 4"Sq. x 1-1/2" box exteneion ring?
    Who said you can't?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    How many and what size conductors are in the box?

    Did the inspector also add the volume of the raised ring?

  4. #4
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    If the inspector told you you needed a larger box then add the box extention...

    BTW...how many wires are in the box?

  5. #5
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    The volume allowance is for a device, not an outlet. See the NEC definition of an outlet. The correct volume is for 2x the wire gauge attached to the device, ie 2 #14 = 4.

    Regardless of being insulated or not the ground still only counts as 1 volume allowance.

  6. #6
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by Ian Gills View Post
    15 conductors I think is the limit if you are using 12 gauge wire in a 4"x2/18" square box, but that's just a guess based on common sense. I am not an electrician..........

    I guess it is the 2 gang that is killing you here........

    I guess 2 duplex receptacles might count as four, depending on how an "outlet" is defined.............

    And your grounds might be insulated. That will push the number up. All uninsulated grounds count as one but each insulated wire is one..............
    All guesses, some wrong, and mostly erroneous.

    Quote Originally Posted by Ian Gills View Post
    But again, I don't really know what I am talking about.
    This part is mostly true.


    Ian, PLEASE try to refrain from posting stuff like this if you are not sure if what you are saying is correct.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  7. #7
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    Sorry Petey I got carried away and made some awful and dangerous assumptions. Thank you for calling me out.

    I just checked some of my boxes and thanks for the ground wire clarification.

    But the whole process can be summarized this way, I think. But again, I don't really know what I am talking about and I am not an electrician.

    1. If conductors are the same size, add them together and size the box using the AWG size columns of Table 314.16(A). Your conductor equivalents will all be the same size as the conductors.

    2. If the box contains different sizes of conductors, use Table 314.16(B) to find the area of each conductor, add them up, and size the box from Table 314.16(A) using the cubic inch column.

    But please remember:

    1. Calculating box volume is a matter of adding up individual volumes of assembled parts [314.16(A)].

    2. Calculating conductor volume is a matter of adding up individual conductor equivalent volumes and there are five of these: 314.16(B)(1) through (5) [conductor volumes, cable clamp volumes, supporting fixture volumes, device yolk volumes and equipment grounding conductor volumes].


    If box fill exceeds box volume, then you need to reduce the number of conductors or use a larger box. You can add to the box volume the sum of individual volumes of assembled parts, such as plaster rings, extension rings, etc. You should however only include only those parts that are marked with their volumes in cubic inches [314.16(A)] or included in NEC Table 314.16(A).

    Keep in mind that these are minimum requirements. There's no penalty for using a box that's too big, other than the additional cost of that box versus a smaller one.
    Last edited by Ian Gills; 09-11-2009 at 06:32 PM.

  8. #8
    DIY Member Ford2001's Avatar
    Join Date
    Sep 2009
    Location
    Manchester, Vermont
    Posts
    32

    Default 4" Sq. ext. box over a 4"Sq x 2-1/8 outlet box

    Your guys are great.

    I just got over a cold.

    But I want to give a big thanks to all, who took the time to reply to
    my Thread.

    Now I just new to replace all the brain cells I burn out when I was
    down with the cold. But your answer have really help me out. (humor)
    Last edited by Ford2001; 09-20-2009 at 06:55 PM. Reason: Sorry should have been Ext. Ring