Double lugging

Users who are viewing this thread

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
As a matter of code I never double lug neutrals in my electrical panel but as a matter of preference I do not double lug grounds either.

Due to a space issue, I may have to start double lugging grounds soon.

My grounds and neutrals share the same bar.

Any comments?
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
You can also go by what the panel manufacturer says in the installation instructions or on the label.
 

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
I double the grounds when needed - same gauges only together
I also tend to "seperate" the grounds & neutrals to make doubling easier if needed
IE I fill the bar from the bottom/top with neutrals, and fill from the opposite end with grounds
 

Jar546

In the Trades
Messages
424
Reaction score
0
Points
0
Location
USA
Website
www.inspectpa.com
You can place 2 grounds under one terminal if:

1) The panel ground bar is rated for 2 wires.
2) The size of the wires are the same where you place 2 under on terminal.
3) The panel ground bar is rated for the size wire(s) you are attaching.
 

Norcal01

Member
Messages
62
Reaction score
4
Points
8
Read the panel listing & labeling, some are listed for as many as 3-EGC's per screw, with a limitation of being the same size, & conductor type. If one runs out of space on a ground bar you can always add a additional ground bar, too.
 