    Default Problem with Laundry Drain. Photos Included.

    First off please excuse my lack of knowledge in regards to plumbing. I've done small jobs here and there, and have helped friends in the past, but I don't claim to know a lot about plumbing.

    Long story short... I had some foundation work done to the house. I was expecting problems to arise because of this. The doors needs to be rehung, and small cracks appeared in the plastic. No problem.

    Basically what looked to be a small leak under the house, is a much bigger problem. The drain for the washer had a small leak on a fitting, but had a much larger problem where it meets up with the main drain of the house.

    I also noticed the whole plumbing job on the washer is wrong so it will need to be completely redone. There is no trap, vent, etc.

    Here is the pipe after I cut it in half. I was amazed at the buildup inside. Is this caused by no vent, or maybe the wrong angle of the drain?


    Where this galvanized pipe (1' 1/2"?) meets the old iron drain. As you can see the problem doesn't get any better. When I checked this area the galvanized pipe could move around inside in the iron pipe.






    A few questions:

    1) I'm planning to redo all the lines for the washer with PVC. How do I properly connect PVC with the iron drain? The supply lines will stay galvanized.

    2) Can the trap for the drain be under the house, or should it be in the wall cavity?

    3) What should the angle of the drain pipe be for maximum efficiency? I'm wondering if this may not have had a good enough angle. If not what would cause this amount of buildup? Could the lack of a vent have caused this?

    Any help would be appreciated.

  2. #2
    DIY Member Henry G's Avatar
    Join Date
    Sep 2009
    Location
    Washington, UPC code
    Posts
    30

    Default

    The rest of that part of the drain system.


  3. #3
    Master Plumber-Gas Fitter shacko's Avatar
    Join Date
    Jan 2006
    Location
    Rosedale, Md
    Posts
    561

    Default Drain Problem

    You have a major problem on your hands, all that cast iron that I can see should be replaced; whoever put it in should be rolling over is his grave!

    The lines are kinked and traped, no wonder they didn't drain properly and allowed that mess to build up.

    Cut the cast until you get to a straight piece, then you can connect pvc with Fernco or Mission couplings, keep in mind all of that pipe needs to be replaced, water lines also if they are galv.

    The wash machine trap has to be near the washer, you can't put it below the floor, it also needs a 18-30in. stand pipe out of the trap, plus a vent, have fun,

  4. #4

    Default

    I sell Real Estate can I interest you in a new house?

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default



    The p-trap needs to be on the same floor as the washer, not below the floor.



    Below the hub you can see the lead we pulled out,
    in the hub is the new 2" pipe with Fernco insert.

    You also have 2" hubs.

    Many times when I pull out old pipe, it looks like that.
    1/4" per foot grade or 2% is what we use.


    This one fits inside a hub, and the pipe is pushed inside.
    I taper the end of the pipe, and lube it with liquid soap.
    Last edited by Terry; 09-24-2009 at 04:38 PM.

  6. #6
    DIY Member Henry G's Avatar
    Join Date
    Sep 2009
    Location
    Washington, UPC code
    Posts
    30

    Default

    Quote Originally Posted by Terry View Post

    The p-trap needs to be on the same floor as the washer, not below the floor.


    Below the hub you can see the lead we pulled out,
    in the hub is the new 2" pipe with Fernco insert.

    You also have 2" hubs.

    Many times when I pull out old pipe, it looks like that.
    1/4" per foot grade or 2% is what we use.
    1. A picture is worth a thousand words! I will follow this example in the photo.


    2. I was reading another thread in this forum and I think I'll try and get these fernco inserts.

    "Fernco donut part numbers for 2" plastic DWV pipe into 2" cast iron hub:
    P22U-205: for service duty cast iron (marked "SV")
    P22UX-205: for extra heavy cast iron (marked "XH")"

    I need to crawl back under the house to check which cast iron I have. Should this marking be easy to find?

    3. I need to install a vent pipe. Should this always be vented through the roof, or are you able to vent it under the eve?

  7. #7
    DIY Member Henry G's Avatar
    Join Date
    Sep 2009
    Location
    Washington, UPC code
    Posts
    30

    Default

    Quote Originally Posted by Cookie View Post
    I sell Real Estate can I interest you in a new house?
    We'll see how this turns out. I may be giving you a call.

  8. #8
    DIY Member Henry G's Avatar
    Join Date
    Sep 2009
    Location
    Washington, UPC code
    Posts
    30

    Default

    Wow, this forum is awesome. I didn't expect any replies for at least a week!

    Yeah I figured I would need to fix this nightmare situation. The problem is I can only cut so much unless I want to also redo the drain to the sink. You can't see it from this picture but there is also a drain line behind it that runs to the sink.

    I plan to do it all correctly but at the moment I need to be able to use the washing machine. I figured that I would correct all the problems in the laundry room, and down to the drain for now. Then tackle the rest.

    I'll look into the Fernco couplings.

    Quote Originally Posted by shacko View Post
    You have a major problem on your hands, all that cast iron that I can see should be replaced; whoever put it in should be rolling over is his grave!

    The lines are kinked and traped, no wonder they didn't drain properly and allowed that mess to build up.

    Cut the cast until you get to a straight piece, then you can connect pvc with Fernco or Mission couplings, keep in mind all of that pipe needs to be replaced, water lines also if they are galv.

    The wash machine trap has to be near the washer, you can't put it below the floor, it also needs a 18-30in. stand pipe out of the trap, plus a vent, have fun,