Thread: Pool tripping GFCI breaker

  1. #1
    In the Trades killavolt's Avatar
    Join Date
    Apr 2009
    Location
    Southington CT
    Posts
    33

    Default Pool tripping GFCI breaker

    A friend of mine has an inground pool. The last few days the pump has been tripping the GFCI breaker. He reset the breaker and the pump would run for a while and now the breaker won't reset. He replaced the pump, I replaced the GFCI breaker, making sure the neutral load was installed on the correct terminal of the GFCI and that the line and neutral were correctly wired in the panel. I replaced the twist lock receptical, with a 20A 125V (same as before) and the 20A switch. I also replaced the bubble rain tight cover as the gasket didn't look as if it was intsalled "rain tight". The GFCI doesn't trip when the pump is not plugged in. The pool and pump are correctly grounded as per NEC code 2008. The pool pump is on a timer if this helps.
    Any thoughts as to what could be causing the GFCI to trip? I took the twist lock pigtail off and installed a regular plug on and the pump runs fine (on another non GFCI circuit) . I taped the twist lock receptical and the switch contacts inside the weather tight box as well to make sure they were isolated from adjacent wires. The pump draws about 18A on a 120V circuit, which is pushing the ampacity of the circuit but it has run this way for about 6 years.
    Last edited by killavolt; 08-04-2009 at 04:01 PM.

  2. #2
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Disconnect the neutral wire from the load side of the GFCI and check for no continuity between it and the ground wire.
    Reconnect the neutral.

    Measure the cold resistance of a 7-1/2w incand. lamp. It should be 100 Ω to 400 Ω. Call the value R.
    Put the lamp in series with the ground wire that serves the cable downstream of your GFCI.
    If the voltage across the bulb reads from 0.004R [0.4v to 1.6v] up to 120vac you've found your leakage path to ground. A normal reading would be 0.0005R for each 100' of Romex downstream of the GFCI.
    Last edited by Thatguy; 08-04-2009 at 06:35 PM.

  3. #3
    In the Trades killavolt's Avatar
    Join Date
    Apr 2009
    Location
    Southington CT
    Posts
    33

    Default

    This is a GFCI breaker, on a dedicated circuit that serves only the pool pump. The neutral and ground buss bars in the panel are not seperated as this is a main panel. I have continuity between the neutral and ground at the pool's twist lock receptacle. I appreciate you taking the time to answer though.

  4. #4
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Better search terms might narrow this down.

    http://www.google.com/search?hl=en&c..._nhi=&safe=off

  5. #5
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Try plugging the motor into another gfci protected circut.
    Test the pool circut with a load other than the pool motor.

    You should have continuity from neutral to equipment ground, they are joined at the service.
    If you take the load neutral off the gfci breaker then check for continuity it should read clear.
    However if you follow the first two suggestions you may not need to do this.

  6. #6
    In the Trades killavolt's Avatar
    Join Date
    Apr 2009
    Location
    Southington CT
    Posts
    33

    Default

    Thanks fellas, I'm going over today to have another look. I'll report back with results.

  7. #7
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    The motor is probably shot. just a stupid guess though.

  8. #8
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by killavolt View Post
    the GFCI breaker
    Can you post a link to the one you are using?

  9. #9
    In the Trades killavolt's Avatar
    Join Date
    Apr 2009
    Location
    Southington CT
    Posts
    33

    Default

    Quote Originally Posted by Chris75 View Post
    The motor is probably shot. just a stupid guess though.
    Replaced the pump motor yesterday brand new Hayward 1 1/2 H.P. I found where someone tied a lighting circuit into the pool's GFCI breaker circuit twist lock 4' sq. I'm gonna disconnect it and try a new pigtail on the pump motor. Water inside the pigtail could cause a ground fault.

  10. #10
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by killavolt View Post
    Replaced the pump motor yesterday brand new Hayward 1 1/2 H.P. I found where someone tied a lighting circuit into the pool's GFCI breaker circuit twist lock 4' sq. I'm gonna disconnect it and try a new pigtail on the pump motor. Water inside the pigtail could cause a ground fault.
    1.5 hp motor at 120volts? highly doubt it.

  11. #11

    Default

    Don't doubt, it they do exist. I have a gould irrigation 2hp running on 120.

  12. #12
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    Quote Originally Posted by Chris75 View Post
    1.5 hp motor at 120volts? highly doubt it.
    My pool pump is 1.5 hp & is switchable from 120 tp 240v
    At 120 it was rated for 18.6a Max - also a Hayward
    So I wired it for 240v
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  13. #13
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by killavolt View Post
    I found where someone tied a lighting circuit into the pool's GFCI breaker circuit
    So for GFCI breaker problems the first thing to check for is bootleg wiring.

  14. #14
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    Actually all of the lights near my pool & in the pool cabana are GFCI protected

    But my pump is on its own circuit - now 240v
    Mine is rated at 18.6a @ 120x, so that only left ~168w for anything else
    So with a 150-300w flood light running that could kick out the 20a breaker
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  15. #15
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    No CB should be loaded that high with a continuous load. You risk it potentially tripping regardless if there's a problem or not. Is that amperage the peak start current, or static while running?
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014