    Default No Room For P-Trap on Washer Standpipe

    I am moving my washer 12' and installing a new 2" drain. Due to the placement of the washer box, a standard off-the-shelf p-trap won't fit without cutting out a large portion of the stud (vertical of p-trap falls in line with stud).

    Is there any reason why a built up p-trap using 90 deg elbows would not be allowed and/or recommended? Also, is there a width limitation on a trap? I would have to extend the width on the bottom of the trap about 3" to pass through the stud.

    Thanks in advance for any comments.

  2. #2
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Why not pass through the stud with the vertical waste and then install the trap?

    Last edited by Terry; 06-02-2010 at 01:49 PM.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,207
    Blog Entries
    1

    Default

    Why not pass through the stud with the vertical waste and then install the trap?
    Exactly.

    Just place the p-trap within the stud space, and use two 45 els up to the box.

  4. #4
    DIY Junior Member DigitalJim's Avatar
    Join Date
    Aug 2009
    Location
    Rochester, NY
    Posts
    11

    Default

    I'll have to check the clearance, but I believe I can do that.

    Thanks!