http://www.engineeringtoolbox.com/pr...pes-d_404.html
http://www.engineeringtoolbox.com/da...ion-d_646.html
You need to know pipe length and height above the opening into the next larger pipe, pipe materials, # of elbows, etc.
|
|
|
Greetings gang and thanks in advance for any help:
we are remodelling our shower and are looking to put in multiple shower heads and some body sprays.
our current drain is 2".
My question is what is the maximum GPM flow that this drain will handle? Also, is there somewhere on line where I can look at the calculations, etc?
Thanks again for any help.
http://www.engineeringtoolbox.com/pr...pes-d_404.html
http://www.engineeringtoolbox.com/da...ion-d_646.html
You need to know pipe length and height above the opening into the next larger pipe, pipe materials, # of elbows, etc.
Last edited by Thatguy; 08-03-2009 at 02:40 PM.
Assuming you don't have anything greater than say 1" pipes supplying water, it should not be a problem. Now, if it is a really large area of shower, you may want a second drain to limit how far the water has to go to get to the drain.
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013
I'm not sure that the links above are an answer, as they deal with pressurized flow, and you're asking about gravity flow.
I think you can get a workable answer, though not exactly to the question you asked, by looking at your code to see how many fixture units it assigns to the shower heads and how many it allows for the drain pipe size. You're going to have to work within that code if you plan to pass inspection.
Here's the IPC as an example, not intending to say it controls for you.
http://publicecodes.citation.com/st/index.htm
Thanks for the help so far, but I remain confused.
Arkansas has adopted the codes in the link. Our house was built circa 2003.
our master bath shower has a 2 inch drain, 1 shower, 1 toliet, 2 sinks, 1 bath tub separate from the shower.
the remainder of our house has 2 additional toliets, 3 additional bath sinks, 1 kitchen sink, and 1 washer.
If I total this up correct with what I have, it comes to 22 units. The rating for a two inch drain if I am reading the table correctly calls for a maximum unit value of 21 for a 2 inch drain with only one quarter inch of slope per foot.
for a slope of one half inch per foot, it apparently allows up to 26 units.
I want to add to my existing master show 1 additional shower head (total of 2), and 4 body sprays. The gpm rating of the two shower heads will be 2.5 gpm each for a total of 5 and for each of the body sprays 1.75 gpm for a total of 7 for the sprays and a grand total of 12 gpm for the entire shower.
When I consulted my plumber this afternoon he said that the maximum GPM for a 2" drain is 12gpm, so according to him this will work.
I would like to get some independent confirmation of this.
Will the above work with a 2" drain?
Thanks again in advance for any help/replies.
I don't want to remodel the entire shower and then not have it drain.
Glenn
I think you're missing something...your toilet drain is at least a 3" pipe, and the whole house may go into a 4" pipe. The outlet of the house drain system is at least 3".
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013