Pump start relay switch - how to test

Users who are viewing this thread

garberfc

New Member
Messages
26
Reaction score
0
Points
1
Location
Connecticut
We had a lighting strike recently that fried both the controller and the pump relay switch. I've been replacing parts as I discover they're not working. Fun :eek:. I'm at the point where everything is working except the pump relay switch (I think).

When the controller signals for water I can see with a volt meter that it's putting out ~26-27 volts AC. I'm measuring across the common and relay out terminals. I'm using a new controller. It's a Cyber-Rain http://www.cyber-rain.com/Products/products.aspx

The pump start relay switch is a AEG SL07 http://www.calcentron.com/Pages/AEGHomePage/aeg_contactors/aeg_contactors_home.htm

My problem is that when I have the controller apply the switching voltage, I don't see the switch close. I'm placing an Ohm meter across one of the pairs of contacts. When I press the switch on the relay next to the "10E" label I do see the switch close.

I've bought two SL07 switches thinking the first was faulty, but I get the same results with the second one. I'm not an electrician so I may be way off base, but is it possible that the voltage is correct, but there isn't enough current put out by the controller to trip the relay?

All thought are appreciated...

F
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
When the controller signals for water I can see with a volt meter that it's putting out ~26-27 volts AC. I'm measuring across the common and relay out terminals. The pump start relay switch is a AEG SL07 http://www.calcentron.com/Pages/AEGHomePage/aeg_contactors/aeg_contactors_home.htm

My problem is that when I have the controller apply the switching voltage, I don't see the switch close. I'm placing an Ohm meter across one of the pairs of contacts. When I press the switch on the relay next to the "10E" label I do see the switch close.

I've bought two SL07 switches thinking the first was faulty, but I get the same results with the second one. I'm not an electrician so I may be way off base, but is it possible that the voltage is correct, but there isn't enough current put out by the controller to trip the relay?

All thought are appreciated...

F
Check the current draw into the contactor coil. It almost certainly is open, but it's unlikely that two in a row have open coil windings. Getting spec's on the coil resistance/impedance/current draw is pulling teeth [lack of info seems to work in favor of the vendor]. You'll probably have to call them.
 
Last edited:

garberfc

New Member
Messages
26
Reaction score
0
Points
1
Location
Connecticut
Check the current draw into the contactor coil. It almost certainly is open, but it's unlikely that two in a row have open coil windings. Getting spec's on the coil resistance/impedance/current draw is pulling teeth [lack of info seems to work in favor of the vendor]. You'll probably have to call them.
Testing things like "Current Draw" are beyond me :confused:. The relay is the same model as the old one. The only component I'm replacing with a different maker/model is the CyberRain controller. That's why I'm thinking it's the controller.

Thanks for the help.