Thread: wiring in bathroom

  1. #1
    DIY Member web_surfer's Avatar
    Join Date
    Jun 2009
    Location
    Wisconsin
    Posts
    38

    Default wiring in bathroom

    Have quick question on wiring a new bathroom.

    We are putting a light in the tub/shower area. The light is sealed against moisture. When the wire was run, UF wire was used since we considered this a damp location due to the high humidity that is typically in bathrooms, especially the tub/shower enclosure.

    Anyhow, the city electrical inspector came through and said NMB would have been OK since light was sealed against moisture and wire would not actually be in damp location. Is this accurate?

    Or maybe since the bathroom is gutted he did not understand exactly what was being done.

    I do have a licensed electrician assisting with the project - installed new 200A panel, tells me where to run wire & i do it, then he connects to panel, etc. He did not say anything about the UF vs NMB being used but, have not talked to him since inspection.

    Thanks,
    Matt

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default wire

    Unless you were hanging the wire exposed inside the shower stall, it was not in a damp location.

  3. #3

    Default

    The inspector is correct. Offhand I can't think of a reason to run UF inside a house.

    -rick

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Not to sound like a jerk, but why would anyone ever consider inside a wall space a damp location???? Same goes for worrying about wires and pipes in the same stud space.

    I think MOLD would be the real issue in that case, no?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  5. #5
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Default

    Quote Originally Posted by web_surfer View Post
    Anyhow, the city electrical inspector came through and said NMB would have been OK since light was sealed against moisture and wire would not actually be in damp location. Is this accurate?
    Thanks,
    Matt
    The inspector is absoutely correct. Any wiring in a wall is not a wet or damp location.