Thread: Roof Mounted Attic Fan on a Dimmer Switch?

  1. #1
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default Roof Mounted Attic Fan on a Dimmer Switch?

    I have an Nutone attic exhaust fan I would like to slow down a bit. Can I put a dimmer switch of some sort on it? Any ideas? They sell similar items to control ceiling fan speed - is that an option?
    Last edited by bjferri; 07-19-2009 at 06:42 AM.
    Brian

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    NO, not a dimmer. You need a motor speed control, but it MUST be rated for the motor it is controlling.

    Verify the amperage of the motor and go to a real electrical supply house and get what you need.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    I have also have a Humidistat and Thermostat connected. Do I need to verify amps of those items too? Where would I make the connection for the motor speed control? I'm trying to find the fan amps as I write this...

    Thanks.
    Brian

  4. #4
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    Found it! 4.3 amps.
    Brian

  5. #5
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Put the speed control last in line before the motor. You do not want to vary the voltage into the two stats.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  6. #6
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    Gotcha! Thanks again!
    Brian

  7. #7
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Putting it is series with an incand. lamp probably won't damage it. Less wattage= more speed reduction.

  8. #8
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    Quote Originally Posted by Thatguy View Post
    Putting it is series with an incand. lamp probably won't damage it. Less wattage= more speed reduction.
    Can you clarify this? I really don't understand...

    Thanks...
    Brian

  9. #9
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    It's a series circuit: a 120v source in series with the lamp in series with the fan.

    If the fan draws 100w@120v and the lamp draws 100w@120v, then when you put them in series each will get half voltage and 1/4th the power, so the fan will move more slowly and the lamp will hardly glow at all.

    The trouble is an incand. lamp has a resistance that depends on the current through it, so you should try different size incand. bulbs until you find one that gives you a satisfactory fan speed.

    With 7-1/2w the lamp will probably glow full brightness and the fan won't move and with 100w the opposite will be true, depending on the fan size.

  10. #10
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    I think I understand, but does this mean I will always have a light burning in the attic?
    Brian

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,376

    Default

    Yes, until the bulb burns out, and then the fan stops. Depending on the motor controller, some act like that and generate a fair amount of heat. Some chop the output.

    You might want to check the motor itself...some have multiple windings, allowing more than one speed. They save money by not wiring them up. All you may need is a 2-3 position switch, properly wired to control speed. If there are more than two wires to the fan motor, look closely at the data plate. You might be lucky. Also, there may be a set of jumpers...those may allow an alternate speed.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    I'm not exactly sure what to look for but am I safe to buy a Motor Rated Fan Speed Control to replace the existing on/off switch? So long as the amps are okay?

    I was also told I may be able to rewind the motor but if it's easier replacing a shutoff switch I'd rather do that. Or but a smaller motor and replace... This is not my forte...

    Thanks again...
    Brian

  13. #13
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    For the cost of rewinding the motor you could buy three fans that run at different speeds.

    Is this a whole house attic fan? The kind that sound like an air plane on the runway? On the fan motor is a Horse Power rating. Find it and post it and you'll get some better advice.

  14. #14
    DoD Army bjferri's Avatar
    Join Date
    Jun 2007
    Location
    Maryland
    Posts
    148

    Default

    It's not measured by HP - it's an attic roof fan measured as CFM. I think my only option is to replace motor and blade assembly. I was told I could replace the on/off switch with a motor rated speed control switch but I'm not sure what it'll do to the humidistat/thermostat.
    Brian

  15. #15
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,376

    Default

    This is probably how those sensors work...they act like a switch. When they sense the proper conditions, they either close or open the switch. So, if that is the case, it's not much different than adding an on/off switch. The motor controller would either have power applied, or not as determined by the switches in series before it.

    the motor probably has a data plate on it...if you post that, someone may be able to tell you what your options are.
    Jim DeBruycker