Connecting to Cast Iron P-Trap

Users who are viewing this thread

gransom

New Member
Messages
2
Reaction score
0
Points
1
Location
Texas
I am replacing a tub, a picture of the P-trap is below. A 1.5" pvc pipe was inserted into the hole. What is the correct way to fit the waste and overflow pipe into this existing hub? There is not enough pipe coming out of the hub to attach an adapter.
 

Attachments

  • 090705 006.jpg
    090705 006.jpg
    71.6 KB · Views: 1,173

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
drain

The correct way is to remove the lead, remove the pipe stub, insert a new pipe stub of the proper length, and then repour the lead joint. Assuming it is in the proper location for the new fixture.
 