A decent manual-D software package would probably tell you the answer. Doing the perimeter approach is probably less work, but may require the perimeter duct to be larger. The trunk & branch approach is what I see most often. (And mastic-sealed seams & joints make an efficiency difference, in either approach.)
But whatever you do, if the mechanicals & ducts are all in the attic, insulating & sealing the attic at the roof deck turning it into semi-conditioned space makes a large difference in operating efficiency (a bigger difference than 14 vs 16 SEER). In a vented attic, any duct leakage results in air infiltration of the worst-sort: Solar-heated attic air than's several 10s of degrees hotter than outdoor air. A sealed & insulated attic is by far the preferable approach, since all potential leakage then occurs inside the insulation & pressure envelope, and the air handler & ducts are then surrounded by room-temperature air, not solar-heat-attic temperature air, so even the conducted losses to the surrounding air go toward cooling the conditioned space, not the overheated attic. See:
http://www.buildingscience.com/docum...s-vegas-nevada
For other considerations/issues around sealed attics see:
http://www.buildingscience.com/docum...d/attachedFile
If it's just the ducts in the attic (and not the air-handler), sealing them with mastic and burying them in a foot of cellulose works too. (Cheaper than foam-sealing/insulating the roof deck.)