Can I install 2 submersible pumps in one 8" well. One pump for household needs and one to feed the water-to-air heat pump.

The well produces 30 gpm at a draw down of 60'. Yje well is 220 ft deep. I want 6 gpm for the household using a 1/2hp submersible (set down at 80') and 7-12 gpm for the heat pump using a 3/4 hp set down at 100'.

Would the 1/2 hp pump starting up wear out the wires from the 3/4 going by?

Any suggestions appreciated.
 
Last edited:

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
Can I install 2 submersible pumps in one 6" well. One pump for household needs and one to feed the water-to-air heat pump.

The well produces 30 gpm at a draw down of 60'. I want 6 gpm for the household using a 1/2hp submersible (set down at 80') and 7-12 gpm for the heat pump using a 3/4 hp set down at 100'.

Would the 1/2hp pump starting up wear out the wires from the 3/4 going by?

Any suggestions appreciated.
There won't be sufficient space but, you will need more than 6 gpm in a house even if you only have one bathroom.

You can't just pick a hp, pumps are sized in two parts, the wet end (gpm) and the motor (hp), so you need to know how many gpm at what elevation and psi, and then the last thing is you find the hp to do the job.
 

dancour

New Member
Messages
9
Reaction score
0
Points
0
2 pumps in one well

Presently, we have a 1/3 hp @ 80' and are operating both the heat pump on stage one and house satisfactorily. I've purchased a Berkerly B15P4MS to replace the 1/3 hp but I thought 2 pumps might work: one operating at 25 psi (HP) and the other at 50 psi (house).

As you say, space may prohibit such an installation. (But I do have a hand pump @ cylinder in the same well which I plan on removing.)
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
It would be hard to get two subs to fit in the well. You can use a 15 GPM, 1/3rd HP pump in the well and a ½ HP jet pump to boost pressure to the house when needed. This way you keep a very small pump in the well for the heat pump. Changing this out to a single1 HP pump would triple your pumping cost. I have written up how to do this before but, can’t find the thread right now. Let me know if you need instructions.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
I found it!

Another way to cut pumping cost which would be easier to control follows. I would use a 16S05-5 pump end, remove 2 impellers, and use a 1/3 HP motor. This pump would deliver 16 GPM at 50' of lift. Control this well pump with a 20 PSI Cycle Stop Valve, a small pressure tank, and a 10/30 pressure switch. After the pressure tank, one line tees off to the heat pump, another tees off to a booster pump for the house. Use about a 3/4 HP jet pump with it's own Cycle Stop Valve set at 50 PSI, and a 40/60 pressure switch.

When the heat pump alone is running, an electric discharge valve opens, the pressure tank drains to 10 PSI, and the pump starts. The 20 PSI CSV will vary the flow to match the 12 GPM usage and maintain 20 PSI. This should cut your pumping cost to 1/3 of what the 3/4 HP is doing now. When the heat pump shuts off, the electric discharge valve closes, and the CSV slowly fills the pressure tank to 30 PSI, and the well pump is shut off.

When the house alone is using water, the pressure will drop from 60 to 40 PSI and the 3/4 HP jet pump will start. The 50 PSI CSV will maintain 50 PSI to the house no mater the flow rate being used. This jet pump system is drawing water from the well pump system, so the pressure tank on the well pump system empties as the pressure drops from 30 to 10 PSI, and the well pump is started. The CSV on the well pump feeds exactly as much water to the jet pump booster as the house is using. Both pumps run as long as the house is using water. When the house stops using water, the CSV on the jet pump will slowly fill the pressure tank to 60 PSI, and the jet pump is shut off. Then the CSV on the well pump will slowly fill it's pressure tank to 30 PSI, and the well pump is shut off.

When the heat pump is running, the well pump/CSV is delivering 12 GPM at 20 PSI. If the house needs water at the same time, the jet booster pump comes on, and the CSV on the well pump opens up to supply both the heat pump and the jet booster pump. Depending on the water level, you should be able to get about 18 GPM total when the house and heat pump need water at the same time. When the house no longer needs water, the jet pump system will fill it's pressure tank to 60 PSI, and the jet pump is shut off. Then the CSV on the well pump reduces the flow to 12 GPM, matching the amount used by the heat pump. Again, when the heat pump is shut off, the well pump fills it's pressure tank to 30 PSI, and both pumps stay shut off until water is needed again.

If the water level in the well pulls down to more than 20' at high flow, you will have to stay with a ½ HP well pump and not remove impellers from the 16S05-5. Even this will cut your pumping cost to half of what they are now.
 

dancour

New Member
Messages
9
Reaction score
0
Points
0
Thanks Valveman for your detailed response … but I like the idea having 2 submersibles in one well for redundancy purposes. With a couple extra lines and valves, I could use either in case of an emergency.

My heat pump runs off the well and I wouldn’t want to have to pull it mid winter.

I’ve also heard that booster pumps are quite loud.

I did find the “Wesley tool†that you mentioned in another posting but it looks expensive.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
You can't get two pumps in the same well with only 6" casing. Even using a Weslly tool you need a lot of detph of water. Maybe you could put a pump in each well, and each well dump to the other. Still need the smallest pump possible for the heat pump to keep pumping cost down.
 

dancour

New Member
Messages
9
Reaction score
0
Points
0
I made an error on the well diameter. It is 8" (not 6") and has a depth of 220' but pumps non stop 30 gpm @ 120'.
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
OK 2 pumps will fit inside 8" casing, but it is still a tight fit. You will have to set one pump just above the other. And if the lower pump quits, you will have to first pull the higher pump before you can pull the lower one.

I still think one pump in each well is a better choice.
 

dancour

New Member
Messages
9
Reaction score
0
Points
0
That's a good point Valveman. I'm not looking forward to pulling my hand pump, just to replace my submersible.
 

Attachments

  • HPump 2b.jpg
    HPump 2b.jpg
    94.3 KB · Views: 1,484

project_x

New Member
Messages
7
Reaction score
0
Points
0
valveman,
I know this is an old thread, but I finally am getting around to reworking my open loop/household water system. Where would I find a 20psi CSV? The lowest I seem to be able to find is a 40psi.

Thanks,
Rob
 

dancour

New Member
Messages
9
Reaction score
0
Points
0
An Update on 2 Pumps in one well.

Yes, it was a tight squeeze getting the 2 pumps in one excellent 8" well. And yes, if the new 3/4 hp Berkeley, set at 100 feet dies first, I'll have to pull the 1/2 hp Franklin.

I did enclose the Berkeley wires passing the Frankin in a 3/4 conduit to avoid wire rubbing.

I've had a Franklin MonoDrive running the Berkeley for my heat pump and house this past year and use the Franklin as backup. With the turn of 2 valves I can switch supply lines thus allowing me to service the pump on my schedule. (It also allows me to flush filters backwards.)

I finally got a hold of a CSV and I'm going to put it on the supply line for the Franklin and see how it runs. In my situation I would like to install it vertically on the line coming in. I'll try running it at 50 psi.

With the wet summer we've had, the pumps haven't had much to do.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
I can get you a 20 PSI CSV but, I would use a 50 PSI valve. That way you can also use it for supplying the house. You are going to need the 1/2 HP backup pump to be able to supply the house as well, because that Monodrive is going to quit soon and leave you out of water at the most inoppurtune time. Here is a quote I got recently from a pump company with decades of experience.

"Hello,
We are faced with a huge vfd push here in our area unfortunately we have been caught up in it as well and now we are realizing that it is just not a good product as far as life of the components are concerned or energy wise. We have used your products in the past and now realize how much of a mistake the vfd can be for repeat business. We would like to become a distributor if possible and help promote your product as well as installing them for our coustomers.
Thanks"
 

Jonrug

New Member
Messages
1
Reaction score
0
Points
1
Location
South Africa
You can't get two pumps in the same well with only 6" casing. Even using a Weslly tool you need a lot of detph of water. Maybe you could put a pump in each well, and each well dump to the other. Still need the smallest pump possible for the heat pump to keep pumping cost down.

Hi. I need a Wesley Tool. Do you know anywhere on the globe I can get one? What is the commercial name?
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Nobody makes the Wesley tool anymore. If you have 8" casing you can still put two pumps in the same well with one set just above the other. If you need a low pressure/high pressure type set up you can use a high volume low pressure pump in the well and add a little jet pump for a booster up top going to the lines that need the higher pressure.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Every time it comes up somewhere, somebody calls me and ask me not to mention it anymore, because they no longer make it. I thought I had deleted any reference to it. Guess I missed one. Anyway it was a device that let you pump two pumps on the same drop pipe.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks