Drain routing in bathroom remodel

Users who are viewing this thread

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
Hello all,
I am currently in the beginning stages of a bathroom remodel (half way through demolition) and would appreciate any input on the layout of my drain lines and vents. I am moving the location of the toilet and sink. The tub is being replaced with a shower with a 2" drain line and the toilet is being moved about 3 feet. The sink is also moving a couple of feet closer to the exterior wall. I am on a concrete slab that is not post tensioned. This area this bathroom is in was originally an attached garage that was converted into a bedroom/bathroom, so the plumbing is not original to the house (house was built 1960, add on was done about 10-15 years ago).

Since I am having to reroute/replace all of the drain lines inside the bathroom, I am going to have to break some concrete. I would prefer not to break any more than is neccesary. If you will note my image below, the green lines are drain lines, and the red ones are vents (this is a single story house). First off, does the routing make sense/pass muster? It will all be sloped 1/4" per foot. There is a 4" drain line outside (top) that the current bathroom pumbing drains into, the new plumbing will tie into this line. Since the sink will be close to the outside wall, my plan is to run its drain straight down throuhg the wall, through the concrete slab, the el to the outside. From there it will then tie into the 4" exterior line. For this drain, I was thinking about boring a 2" hole in the concrete slab to run the 1.5" drain line. Since it is only about 18 inches form the exterior, it would be pretty easy to simply dig from the outside to install the el and remaining pipe.

I would knock out a trench from the shower drain to the toilet flange, using 2" line (with p-trap of course) for the shower, then connect that to the 3" line for the toilet. For the vents for the shower and toilet, I was thinking about again boring a 2" hole for each and run them up and into the attic. Currently, each fixture has a 1.5" vent that is tied together in the attic, then a single 1.5" vent protruding through the roof. I have heard that newer toilets should use a 2" vent, but have also seen on this forum how a single 1.5" vent could be sufficient. If I could tie all the vents together and utilize the existing 1.5" vent, that would be great. If not, I am willing to do what it takes to build it properly. Thanks in advance for everyone's help!
 
Last edited:

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
OK, for some reason the picture doesn't show up, lets try that again...
 

Attachments

  • drains.JPG
    drains.JPG
    33.9 KB · Views: 2,104

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
No vent pipes or portions thereof may run horizontally until they have risen 6" above the flood level rim of the highest branch fixture ( in this case the lav) So as drawn, both the shower and the toilet vent are not good. Additionally, if you are under the IPC code, you do not have to directly vent the toilet. The distance fom toilet to vent is "unlimited"
 

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
This would be code compliant in FL and I believe elsewhere IPC is in effect.
3" to toilet, 2" to shower, 2" to lav with 2" vent.

Taking lines outside means going under or through foundations, cutting concrete isn't a big deal.

drains-x.jpg
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Dwv

You do not show how deep the main sewer line is, nor if any of these walls are over the concrete foundation walls. With enough depth, and no walls there are much better configurations.
 

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
OK I get it now. I moved the drainlines so that the vent would rise vertically from it. That also means I would only need 1 vent for the shower and toilet, correct? I am under IRC here.
 

Attachments

  • drains2.JPG
    drains2.JPG
    35.7 KB · Views: 1,939
Last edited:

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
Scratch my reply above, I did not see your response until after I submitted it.

As far as the concrete foundation walls, I do not believe they are very deep, perhaps 6" deeper than the foundation slab itself. Outside where my 4" line is, it is probably another 12" down. I will take a picture and some measurements as soon as I get home today.

From the looks of your diagram, I would only need one vent, at the lavatory?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Vents from multiple fixtures may join into one, but as noted, they must rise high enough first so that they don't become an alternate drain for any of the other fixtures connected to them. generally, this is considered to be 6" above the flood rim of the highest fixture. The other major consideration is the number of fixtures will determine the size of the vent required once they all come together. In cold areas, it may also have to be larger going through the roof so it doesn't get clogged by frost from the rising moist air.
 

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
I snapped a picture of the drain outside, it is hard to tell, but the top of the drain line in the picture is about 18" from the top of the foundation, the base of the foundation footing is about 4" or so above the top of the drain line, so there is some wiggle room. The thing that is running left to right is actually a tree root.
 

Attachments

  • Drain outside.jpg
    Drain outside.jpg
    53.8 KB · Views: 1,917

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Dwv

If the drain line were deep enough AND the distance from the sink to the shower drain was within limits, I might put the vertical pipe behind the sink and then run an arm to the toilet, using a side inlet sanitary tee, another one to the shower drain. But I would not run the lavatory outside as a separate pipe, unless there is some reason not apparent in your drawing. The way you have it configured, the lavatory probably could not be used as the toilet/shower vent.
 

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
The only reason I was thinking about running the drain for the lavatory outside as a seperate pipe was that I figured I would cut less concrete that way. Everyone says that cutting concrete isn't that hard, so maybe I am just worrying about that part too much. One thing that I neglected to mention, the current 4" drain pipe form the outside, connects to the bathroom right in the middle of the upper wall. I have not dug enough of the yard up (triple digit weather) to see where the line goes or how far out from the house it is, but I don't except that to be a major issue. I have attached two more layouts based on the helpful information and suggestions you all have provided (many thanks!). This bathroom is only 7' by 7' (roughly), but I have added a vent at the upper wall in these drawings.
 

Attachments

  • drains3.JPG
    drains3.JPG
    28 KB · Views: 1,833
  • drains4.JPG
    drains4.JPG
    26 KB · Views: 1,772

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
OK, so the 2" vent at the lavatory would be sufficient. besides that, would either of the two layouts above be correct?
 

Kingsotall

Plunger/TurdPuncher
Messages
1,238
Reaction score
1
Points
0
Location
Flagstaff, AZ
Drilling concrete is not that hard...if you have a rotary hammer and preferably core bits. Although punching a bunch of smaller holes also works. But mind you these are specialized tools. The bigger the tool the better, too.
 

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
Both are correct, I usually design to take the largest pipe straight towards it's fixture, the toilet in this case, but that's a matter of preference.

If the wall that the lavatory is going on is a frame wall then you can head straight to it and branch over in the wall for the trap, again that's a matter of preference.
 

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
I hope everyone had a good 4th, and thank you all for your help. I am back again in need of more advice

After showing my wife the bathroom layout I was planning, I have had to make a few "revisions." attached is the new "approved" layout with the green lines representing the drains and the red being a 2" vent. Everything drains into the existing 4" line on the upper wall. I hope this layout is correct, as I have tried to apply what I have learned so far into this design (again, not to scale)
 

Attachments

  • drains6.JPG
    drains6.JPG
    25.1 KB · Views: 2,288

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
Hey guys, I wanted to confirm that I am proceeding in the right direction before I bust anymore concrete. Here is a photo of where I am at now. My cheesy paint job didn't come out as clearly as I hoped. In red is the 2" wet vent where the single vanity will go.
 

Attachments

  • Bathroom layout.jpg
    Bathroom layout.jpg
    54.8 KB · Views: 1,096

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
Also, what do yall recommend I do with the existing lines under the slab? I was planning on cutting them as much as possible with a dremel tool but just leave most of them in place. Should I pack them with sand first?
 

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
Your routing looks good, here we can leave the pipes in the ground. I've seen some inspectors want grout poured in the line but that's impractical and if part of the system is existing to remain will cause problems.
 

austintx

New Member
Messages
27
Reaction score
0
Points
1
Location
World
Removing some of the concrete has revealed some complications. it looks like there is a concrete footing that runs along the wall I was goign to put my vanity on (this is an interior wall). it looks to be about 12" thick. That is a bit more than I expecting, so would it be feasible to run the drain along the wall about 18", 90 degrees, another 12" to the wet vent, like pictured below?
 

Attachments

  • new routing.jpg
    new routing.jpg
    43.2 KB · Views: 1,030