Thread: GFCI Outlet Trips with Lights or Fan Switch

  1. #1
    Electrical Engineer jdf405's Avatar
    Join Date
    Jan 2008
    Location
    Los Angeles Area
    Posts
    45

    Default GFCI Outlet Trips with Lights or Fan Switch

    My bathroom was remodeled about a year ago, with a new 20A line pulled from the panel. The lights and fan are on the line before the GFCI outlet. We leave a rechargable tooth brush plugged into the GFCI all the time, but nothing else.

    Recently when we turn off the lights or the bath vent fan the outlet trips (GFCI, not the 20A breaker). It resets right away easily. All of the wiring was per code, inspected, etc... and I've tested the resistance from hot & neutral to ground with an Ohm meter and its above 1 MOhm (the highest my DVM can read).

    Any ideas on why this happens? Possibly a defective outlet?

    Thanks for the help,
    Jonathan

  2. #2
    DIY Member 1960 rancher's Avatar
    Join Date
    Mar 2009
    Location
    priming pump
    Posts
    38

    Default

    Your stating that the outlet trips when shutting off the light or fan? Seems odd but it could put a surge on the neutral causing the outlet to trip. I would replace the outlet and or confirm there is not a short between the neutral and ground. Not sure what the threshold is for a trip but it could be around 1mega ohm.... If your meter does not go to OL (everload or open) then that could be your problem. Is the tooth brush unplugged when taking this reading?
    Last edited by 1960 rancher; 06-23-2009 at 11:07 AM.