Trap must be below the fixture drain.
|
|
|
I need to install bathtub on the floor where ther is no space for P-trap.
How far from a tub drain can the trap be located?
That is, can I run a horizontal drain for 3 feet (at about 1 inch drop) and install a P-trap and a vent 3 feet away from the tub drain?
Or is it asking for trouble?
Trap must be below the fixture drain.
Matt
Semi-professional plumbing designer
Enjoying life in SW Florida
?
I paid a Master Plumber and he installed the P trap 3 feet away.
I don't think "code" requires it to be under the tub drain.
A couple years ago I installed a sink Ptrap a few feet away from the sink drain and I got input here from hj terry and others on how to do it.
You're right, I looked back at the code again.
This is 2009 Florida Plumbing Code, it is similar and sometimes identical to the IPC.
1002.1 Fixture traps. Each plumbing fixture shall be separately trapped by a water-seal trap, except as otherwise permitted by this code. The vertical distance from the fixture outlet to the trap weir shall not exceed 24 inches (610 mm) and the horizontal distance shall not exceed 30 inches (610 mm) measured from the centerline of the fixture outlet to the centerline of the inlet of the trap
Matt
Semi-professional plumbing designer
Enjoying life in SW Florida
There will be a (hopefully small) accumulation of soap scum, body oils, dead skin, etc. build-up on the walls of the pipe. 3' of that can smell pretty raunchy. That's why the better location for the trap is right under the fixture...the water in the trap blocks not only traditional sewer gasses, but the smells from the drain line going there.
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013
30 inches is 762 mm. A limit has to be imposed at some point. Stretching it is a normal human endeavor.
If this quote was retyped, it's data entry error.
If it's copied, it's a typo in the original document.
24 inches (610 mm)If I were you, I'd measure everything in metric and allow myself a margin of error in my favor.
30 inches (610 mm)![]()
Distance of Trap to Fixture. The developed length from the fixture outlet to the trap weir shall not exceed 24 inches, except when an interceptor is used as a trap, it shall be located as close as possible to the fixture. The maximum developed length from the fixture outlet to the inlet of the interceptor shall not exceed 5 feet. (See Appendix D: Illustration B.) The standpipe inlet for an automatic clothes washer shall not exceed 48 inches above the weir of a trap.
So your best bet is to contact your local building department and ask the plumbing inspector there what they require locally. State codes are the bare minimum, which means counties, townships, and cities can make the code even tougher.
Last edited by SewerRatz; 06-05-2009 at 05:10 PM. Reason: Add a blurb