Main Disconnect Seperate from panel?

Users who are viewing this thread

Nate R

Member
Messages
473
Reaction score
0
Points
16
Location
Milwaukee, WI
When you have an outdoor main disconnect; and the main panel is separate from that (indoors), is the main panel treated as a subpanel as far as neutral/ground bonding?

Where in the NEC do I find this?

Just looking for a quick answer. I was asked this, and I don't know the answer.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
Yes, the panel would be treated as a "sub-panel" with the neutral not bonded.

Here is the NEC section:

250.24(A)(5)Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non–current-carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.
 

Nate R

Member
Messages
473
Reaction score
0
Points
16
Location
Milwaukee, WI
Thanks! My brother is a home inspector. He's doing a pre-sale inspection for the seller to be able to show buyers, and to tell the sellers what may come up and be an issue, etc. He asked me about this, but I wasn't sure.

And thanks for the code section for the quote! :D
 

VinceS

New Member
Messages
1
Reaction score
0
Points
0
That's the problem with home inspectors!

"Thanks! My brother is a home inspector. He's doing a pre-sale inspection for the seller to be able to show buyers, and to tell the sellers what may come up and be an issue, etc. He asked me about this, but I wasn't sure."

Nate R, I realize it was your brother who asked the question, but doesn't that strike you as being a major problem? Your brother is a home inspector and he doesn't know the answer to that question? Unfortunately I've used home inspectors on at least two home purchases, and although they had slick marketing and reports they simply did not know what they were talking about. Unfortunately your brother seems to be in the wrong line of work...that is if he cares about providing a valuable service to his customers.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
inspector

At least he knew enough to ask the question. Most would not bother with it unless it was something that hit them between the eyes with a 2x4.
 

Drick

In the Trades
Messages
460
Reaction score
19
Points
18
At least he knew enough to ask the question. Most would not bother with it unless it was something that hit them between the eyes with a 2x4.

Ain't that the truth!
 