    Default electrical wires near shower

    whats the code on this? - I looked at a rental for sale, it had a one piece stall shower backing up of course to a wall. In the wall was the main service panel (which opened into the next room, the laundry room). The main feed to the service panel came from the crawl space below the house and went up from the floor within a few inches of the plastic bottom of the shower stall.
    Is this OK?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    It's okay.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Member edwardh1's Avatar
    Join Date
    Jul 2006
    Location
    South Carolina
    Posts
    67

    Default

    Is the typical service cable- 80s vintage "waterproof" from casual water like a shower pan leak? this is a grey plastic wrapped service cable with 2 or 3 black power leads that go eventually to the bus bars in the power panel.
    Is it ok for this entrance cable to run under a shower or near a shower pan?

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    That cable is FINE as jadnashua said. That is SE cable and can be run outdoors in direct weather. There are no limitations as to being near shower wall or stall.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  5. #5
    DIY Member edwardh1's Avatar
    Join Date
    Jul 2006
    Location
    South Carolina
    Posts
    67

    Default

    How about ROMEX®- there are two ROMEX® leads there too
    Last edited by Terry; 12-07-2011 at 10:16 AM.

  6. #6
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Same goes for NM cable.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.