Outdoor sub-panel for pool
ddennis
I have to travel to the in-laws this weekend to install a sub-panel for their new above ground pool in the state of Louisiana. Here is my assumptions please tell me if I am wrong or off-base.
Plan is to install a 50 amp sub-panel (outdoors) on a 4' high post near pool.
Water-tight flex containing 4 runs of 4# copper, 2 hot, 1g 1N. 50amp breaker in main, 50 amp main breaker in sub-panel and smaller breakers (gfci) to the loads.
Will a ground rod be needed or do I tie the ground back to the house panel?
Alectrician
DIY Senior Member
#4 is overkill unless it's 3oo' from the source.
Three #8's and a #10 ground will suffice for a 50 amp pool sub. A lot of in ground pools here use a 30 amp feed to a pool sub which covers a filter pump motor, a cleaner pump motor and the pool light(s).
No G rod necessary here. Local ordinances may vary.
Speedy Petey
Licensed Electrical Contractor
NY State, USA
What type of "water tight flex" are you considering? I assume this will be underground.
How close to the pool were you considering? The panel CANNOT be closer than 10' to the pool.
A ground rod is required since this is a detached remote feeder and panel. If the panel were in the same structure as the main no ground rod would be required.
You are also required to run an insulated ground with the feeder conductors in conduit completely back to the main panel.
I REALLY think you need to read up on the codes involved with wiring and bonding for pool equipment.
Alectrician
DIY Senior Member
yes a ground rod is required. read article 250.32
I was assuming a rod wasn't requires because I have never seen one and I have never installed one.
We have lots of pools here. I have seen a hundred pool panels and installed maybe a dozen.
No exceptions anywhere???
Here's my pool. It's about 5 years old and the landscape is starting to really take shape.
ddennis
This is an above ground pool, all 120v equipment. roughly 110 feet to the main panel on the house. I do intend to bury the line minimum of 18 inches deep. NEC calls for the subpanel to be 10 feet from the pool?
A
Apostile
Guest
I have a 60 amp breaker on my main panel connected by 120' of #4/2 with a ground wire. The black and white wires are connected to the load lugs of the sub panel and the ground wire is attached to the neutral block. The outdoor panel box has 2 - 30 amp GFI breakers. One goes to an outlet for the chlorinator; one to the pump motor. The neutral bar is not bonded to the panel. Do I need to add a bonded grounding bar and a grounding rod at the sub panel? Is there any way to correct the grounding of the box without digging up the wire and adding a fourth (common) wire from the main?
Speedy Petey
NY State, USA
No, not at all! What you have is extremely unsafe. You need an insulated neutral run with this feeder. The bare wire in the 4/2 cable should NOT be carrying all the current imbalance.
You need to re-run that cable. If this panel is in a detached structure then you should have already had a ground rod there.
PS- Next time start a new thread with your question instead of tacking it on to an existing thread.
ddennis
OK Speedy.. 3 8's and a 10#... 2 8's to the load bars, 1 8 to the neutral in the main panel .. #10 to the ground rod at the sub-panel..?
Speedy Petey
NY State, USA
You need a ground from the main panel to the sub-panel. Yes, in this case also #10.
You then also need a #6 (if you can believe it) from the ground bar in the sub-panel to a ground rod. You can use a #8 to the ground rod if you can keep it completely out of harms way.
Speedy Petey
NY State, USA
You could claim interpretation of this section, but I think most inspectors would require a ground rod even if the panel were simply mounted to a post.
Alectrician
DIY Senior Member
That's what I'm going with. Like I said, in my area they are not requiring rods.
I didn't read the whole section but saw "building or structure" and figured pool panels were exempt unless the equipment was in a pool house of some kind. The pool electrician guys generally mount them on a small rack made from a couple pieces of 1/2 rigid, the same type of conduit they use to feed it.
Jim Port
Maryland
www.manta.com
You will also need to install all the proper bonding for the pool and the surrounding walk surface.
Like Petey said, there is a lot to a pool or hot tub install. This really isn't the place to screw up.
quote; You are also required to run an insulated ground with the feeder conductors in conduit completely back to the main panel.
That would only be true if there were ANY 120v. circuits. If they are all 240v, such as motors, there will not be ANY imbalance.
Jim Port
Maryland
www.manta.com
I believe Petey was talking about a grounding conductor, not a grounded conductor. Pools and hot tubs installed outside require the grounding conductor to be insulated. 680.21.
CodeOne
Code Enforcement
North Carolina
680.25 Feeders. These provisions shall apply to any feeder
on the supply side of panelboards supplying branch circuits
for pool equipment covered in Part II of this article and on
the load side of the service equipment or the source of a
separately derived system.
(B) Grounding. An equipment grounding conductor shall
be installed with the feeder conductors between the grounding
terminal of the pool equipment panelboard and the
grounding terminal of the applicable service equipment
or
source of a separately derived system. For other than (1)
existing feeders covered in 680.25(A), Exception, or (2)
feeders to separate buildings that do not utilize an insulated
equipment grounding conductor in accordance with
680.25(B)(2), this equipment grounding conductor shall be
insulated.
(1) Size. This conductor shall be sized in accordance with
250.122 but not smaller than 12 AWG. On separately derived
systems, this conductor shall be sized in accordance
with Table 250.66 but not smaller than 8 AWG.
CodeOne
Code Enforcement
North Carolina
How deep is this above ground pool?