Thread: 120V walkway lights linstallation

  1. #1

    Default 120V walkway lights linstallation

    I have a half dozen 120V 3 tier pagoda lights I'd like to install along a new walkway what I am building. I guess the question to you is how would you do this? I could run 1/2 inch SCH 40 between buried bell boxes and mount the light on top of a relatively short pipe nipple off of the bell boxes, but those bell boxes aren't going to be water tight and under the ground and I think that would be a problem. Maybe it doesn't matter if I run THWN and use silicon filled wire nuts. I could cement over the entire bell box. That would make it water tight, but it would be a PITA to replace a broken light.

    Or should I just forget that whole mess and go with UF wire, silicon filled wire nuts and perma posts http://www.berkeysupply.com/product-714.html ? I initially thought this didn't meet code, but now I'm not so sure.

    Or something else maybe?

    -rick

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    The boxes cannot be buried or below grade at all. Also, the PVC alone cannot support the boxes.

    Quote Originally Posted by drick View Post
    Or should I just forget that whole mess and go with UF wire, silicon filled wire nuts and perma posts http://www.berkeysupply.com/product-714.html ? I initially thought this didn't meet code, but now I'm not so sure.

    Or something else maybe?
    This is what I would do. I am partial to Arlington's Garden Post. They have a provision for a receptacle if you want. That or the box can be blanked off. Either way the splice is accessible without removing the fixture.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3

    Default

    In the olden days I would:

    Cut pieces of 2" PVC/ABS as short/long/high/low as you'd like.

    Notch the 2" stubs to clear the PVC 90's and cement/mortar them in place.

    Drill a 1/2" hole in a 2" cap and mount the fixture with a short/close nipple.

    Now they make Rocket Posts/ Perma Posts.

    I have also installed PVC jboxes in the ground, slightly above grade and installed the fixtures on nipples into the appropriate jbox cover. This method leaves the fixture/hardware very vulnerable to damage in most applications.

  4. #4

    Default

    Thank you for the replies. I had not seen the Garden Posts before. They are much nicer looking than a jbox above ground. Anyway I'll either go with those or the Perma Posts.

    -rick