Thread: Distance to stack

  1. #1

    Default Distance to stack

    I'm doing remodeling and am looking at a plumbing book which says that the maximum distance to the stack for a two inch drain is five feet. Does that mean the max distance without a vent or, the max distance period? That seems awfully restrictive. I've seen some incredibly long drain lines.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    That measurement is from the p-trap to the vent.

    The reason for putting vents within certain distances, is so the traps don't siphon out when water is run.
    Last edited by Terry; 07-22-2005 at 09:07 AM.

  3. #3

    Default

    Okay Terry, that makes sense. Just to make sure my understanding is correct: I can have a two inch sink drain eight feet from the main drain as long as the vent from that drain is no more than five feet from the stack. Is that right?

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    P-trap to the vent.

    After you have vented the p-trap, you can go as far as you like.

  5. #5

    Default

    Okay Terry, now I realize I read your first response incorrectly. Please bear with me here, I want to make sure I get it.
    Do I understand correctly that the vent can also be as long as needed? In other words, my sink is eight feet from the main drain. I can connect my vent to the drain line after the P trap and run that vent to the stack. Even though the vent pipe may be more than five feet away from the stack, it is effectively part of the stack since there is nothing ihibiting it between the connection to the drain and the stack. Is that correct?

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The distance from the P-trap to the vent is the critical one. The vent can be anywhere from right next to the P-trap to the max allowed. The distance to the stack is irrelevant, as long as it has the proper pitch.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7

    Default

    Thanks for the clarification, now I've got it.

  8. #8

    Default

    I know I'm digging up an older topic here, but is there a MINIMUM distance from the stack to the vent? For example, I want to put the stack and vent within the same 16" stud distance, but because of some other conditions, my vent pipe tee may only be 2-4" away from the sanitary tee that connects to the vertical stack. This vent would be on a 2" line that ran about 18" to a p-trap servicing a clothes washer.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    No minimum....vent above, drain below could be an extension of the same pipe.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default vent

    We might have to see what your plumbing looks like, because if the vent is that close to the vertical riser it may not need a separate vent, depending on other conditions which we do not know about.