I am considering getting a fujitsu mini-split system. If I get a cooling only unit it has a seer of 14.3. A unit with a heat pump would cost $400 more, but have a seer of 21.0. Is it worth spending the extra money for a higher seer rating? I would probably not use the heat pump, just need cooling. TIA
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
It could probably pay for itself in short order. Take a close look at the current draws, and compare. The scale is linear, so you're getting a nearly 50% increase in efficiency. Now, I'm not fully familiar with how they rate it when it is a heat pump...it may be the same thing as the a/c only version...just factoring in the increased efficiency when in heating mode. If that's true, it isn't worth the difference if you don't need heat. Do they list cooling only efficiency?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Double check the spec sheet. The heat pump may be 21 on heat, and something less on cool. But if it is 21 on cool, the energy savings are significant, and I suspect the cost difference is also large. SO you have to calculate your operating cost over say 5 years vs. the price difference.

Depending on your application, the LG flex multizone units, with inverter-driven variable speed compressors are terrific.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
from Wiki

". . .consider a 5000 BTU/h air-conditioning unit, with a SEER of 10, operating for a total of 1000 hours during an annual cooling season (e.g., 8 hours per day for 125 days).

The annual total cooling output would be:

5000 BTU/h * 8 h/day * 125 days = 5,000,000 BTU
With a SEER of 10, the annual electrical energy usage would be about:

5,000,000 BTU / 10 BTU/W·h = 500,000 W·h
The average power usage may also be calculated more simply by:

Average power = (BTU/h) / (SEER, BTU/W·h) = 5000 / 10 = 500 W
If your electricity cost is 20¢/kW·h, then your operating cost is:

0.5 kW * 20¢/kW·h = 10¢/h"

Seems like you need to first specify the size of the unit. Also, in general, more complexity = less reliability (= higher SEER).

If your yearly cooling is 50 Therms then the 14.3 would use 350 kwh, with the 21.0 using 238 kwh.
If you pay $0.15/kwh then your cost for the 14.3 is $53/yr and for the 21 is about $36/yr.
53-36 = $17/yr, so it would take $400/($17/yr) = 24 yrs to make up your $400.
At 500 Therms/yr it'd take 2.4 yrs.

Do you know how many kwh you use for cooling each year? You may be able to figure it out using the cooling degree day data on this site
http://www.degreedays.net/
plus your yearly elec. bill record.
You'll also need
http://www.google.com/search?client=safari&rls=en-us&q="heat+gain"+house&ie=UTF-8&oe=UTF-8
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks