This is what I found on a search
So 6" above the point where it exits the roof is OK?
I also want to box this in to "hide" it somewhat as it will be viewable from the front
So 6" above the point where it exits the roof is OK?
I also want to box this in to "hide" it somewhat as it will be viewable from the front
Here is the code, CPC sect. 906.1, Each vent pipe or stack shall extend through its flashing and shall terminate vertically not less than six (6) inches above the roof nor less than one (1) foot from any vertical surface.
And CPC sect. 906.2, Each vent shall terminate not less than ten (10) feet from, or at least three (3) feet above, any openable window, door, opening, air intake, or vent shaft, nor less than three (3) feet in every direction from any lot line, alley and street excepted.