Vent pipe termination distance over roof?

Users who are viewing this thread

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
This is what I found on a search
So 6" above the point where it exits the roof is OK?
I also want to box this in to "hide" it somewhat as it will be viewable from the front

Here is the code, CPC sect. 906.1, Each vent pipe or stack shall extend through its flashing and shall terminate vertically not less than six (6) inches above the roof nor less than one (1) foot from any vertical surface.

And CPC sect. 906.2, Each vent shall terminate not less than ten (10) feet from, or at least three (3) feet above, any openable window, door, opening, air intake, or vent shaft, nor less than three (3) feet in every direction from any lot line, alley and street excepted.
 

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
That would help
It's the existing vent stack for plumbing
There is one on each side of the house
Other side has 2 bathrooms- 2sinks/showers/toilets
This side has kitchen sink

Addition has been added on this side of the house
So the stack needs to go up higher then the new roof

Interesting that the old location was very close to a bedroom window that opened & gable vent
 

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
This is from the Illinois plumbing code. I hope some of the items in it are helpful.

Section 890.1430 Vent Terminals
a) Roof Extensions. Extensions of vent pipes through a roof shall be terminated at least 12 inches above such roof unless a roof is to be used for any purpose other than weather protection. If a roof is to be used for any purpose other than weather protection, the vent shall be extended at least seven (7) feet above the roof. (See Appendix K: Illustration D.)

b) Flashings. Each vent terminal shall be made water-tight with the roof by proper flashing.

c) Location of Vent Terminal. No vent terminal from a drainage system shall be directly beneath a door, window, overhang or other ventilating intake opening of the building, nor shall any such vent terminals be within 12 feet horizontally of such an opening unless it is at least two (2) feet above the top of such opening. (See Appendix K: Illustration E.)

d) Extensions Outside Building. No soil, waste or vent pipe extension (except for vent terminals as provided in (a) and (c) above) shall be located on the outside of a wall of any building, but shall be installed inside the building. Vents located within an exterior wall or in a wall adjacent to an unheated space shall be protected from freezing.

e) Flag poles. Vent terminals shall not be used for the purpose of supporting flag poles, television aerials, or similar purposes.​
 

Attachments

  • Ap_k_IL_k.gif
    Ap_k_IL_k.gif
    13.1 KB · Views: 32,367
  • Ap_k_IL_e.gif
    Ap_k_IL_e.gif
    24.2 KB · Views: 11,538

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Note you need to take into account the pitch of the roof, as shown in one of the diagrams, to determine the height above. This would normally mean it must be more than indicated at the point of penetration unless it was a flat roof.

You'd have to talk to the inspector about boxing it in as that would create other problems, and might mean it would still have to exit even higher. You want it above the anticipated maximum snow depth on the roof, too, so that may help dictate the height.
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks