Thread: Troubleshooting two 3-way switch setups

  1. #46
    DIY Junior Member Sinestro's Avatar
    Join Date
    Aug 2011
    Location
    Va
    Posts
    5

    Default

    Quote Originally Posted by jwelectric View Post
    Anyone who answers this question will have their post deleted.

    Light bulb testers are death in a socket and unsafe advice will be deleted.
    Oh lord thanks. Is there a safe way to test out which wire is which? I have no idea which wire is which.

  2. #47
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,679

    Default

    Quote Originally Posted by jwelectric View Post
    Anyone who answers this question will have their post deleted.

    Light bulb testers are death in a socket and unsafe advice will be deleted.
    Does that include my little pocket screwdriver with a neon bulb in the handle one end of which is wired to the tip and the other end to the pocket clip that touches the hand?

  3. #48
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Sinestro View Post
    Oh lord thanks. Is there a safe way to test out which wire is which? I have no idea which wire is which.
    Quote Originally Posted by Sinestro View Post
    Oh lord thanks. Is there a safe way to test out which wire is which? I have no idea which wire is which.
    Most untrained people who dabble in electrical work should never use a meter for any reason. Let me repeat, most untrained people who dabble in electrical work should never use a meter for any reason!
    What most people don’t understand is that the meter they hold in their hand is one of the most dangerous tools they have

    Most people as well as a lot of trained electricians think that the fuse in a meter will protect them from harm. In 99.9% of the cases the fuse only protects the current function of the meter. See the drawing on the meter in the posted picture.

    Meters come with a category rating marked on the meter. For testing voltage in a 240 volt panel with a maximum short circuit of 25ka and a fault clearing time of .033 second I will use nothing less than a category IV meter. After I am about 30 feet from the service disconnect (this is measured along the path of the conductor) I will drop to a category III meter. The meter must have a rating of at least category II for me to check the voltages on switches and receptacles. A meter rated at category I can be used by the electronics tech as I won’t use one.

    ANY METER THAT HAS NO CATEGORY RATING GOES IN THE TRASH INCLUDING NON-CONTACT AND LIGHTED METERS!!!!

    The one thing I can promise is that once one has been involved in a flash over their respect for electrical energy will change, mine did.

    I have said for years you can tell when someone knows what they are doing by looking at their tools. The use of meters tells me just how qualified someone is doing electrical work. I have turned many away just because of their meters.


    Last edited by jwelectric; 08-23-2011 at 01:23 PM. Reason: speling

  4. #49
    DIY Junior Member Sinestro's Avatar
    Join Date
    Aug 2011
    Location
    Va
    Posts
    5

    Default

    Quote Originally Posted by jwelectric View Post
    Most untrained people who dabble in electrical work should never use a meter for any reason. Let me repeat, most untrained people who dabble in electrical work should never use a meter for any reason!
    What most people don’t understand is that the meter they hold in their hand is one of the most dangerous tools they have

    Most people as well as a lot of trained electricians think that the fuse in a meter will protect them from harm. In 99.9% of the cases the fuse only protects the current function of the meter. See the drawing on the meter in the posted picture.

    Meters come with a category rating marked on the meter. For testing voltage in a 240 volt panel with a maximum short circuit of 25ka and a fault clearing time of .033 second I will use nothing less than a category IV meter. After I am about 30 feet from the service disconnect (this is measured along the path of the conductor) I will drop to a category III meter. The meter must have a rating of at least category II for me to check the voltages on switches and receptacles. A meter rated at category I can be used by the electronics tech as I won’t use one.

    ANY METER THAT HAS NO CATEGORY RATING GOES IN THE TRASH INCLUDING NON-CONTACT AND LIGHTED METERS!!!!

    The one thing I can promise is that once one has been involved in a flash over their respect for electrical energy will change, mine did.

    I have said for years you can tell when someone knows what they are doing by looking at their tools. The use of meters tells me just how qualified someone is doing electrical work. I have turned many away just because of their meters.


    Boy thanks I appreciate the warning! Which brings me to my next question. Since I am unqualified to do this, about how much does it normally cost to troubleshoot and fix 3way lighting issues? I want to make sure I don't get fleeced. Thank you again for your help.

  5. #50
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Sinestro View Post
    how much does it normally cost to troubleshoot and fix 3way lighting issues? .
    The best way to answer that question is to say, as much as the market will bear.

    The hourly prices will as much as $25 different within 50 miles radius of where I live.

    If I am paying an electrician $30 an hour it will cost me over $40 an hour to give it to him. Therefore I must receive at least $55 an hour for that man to come out with a profit.

    Any service call I go on will waste at least half a day so if I don’t get at least $250 for that service call I am going broke real fast.

    It will cost as much as you are willing to pay.

  6. #51
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Check out this link for more about testing for voltage

    http://www.iaei.org/magazine/2008/07...urvival-guide/

  7. #52
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by Sinestro View Post
    Boy thanks I appreciate the warning! Which brings me to my next question. Since I am unqualified to do this, about how much does it normally cost to troubleshoot and fix 3way lighting issues? I want to make sure I don't get fleeced. Thank you again for your help.
    I can't tell you how much the job will cost, but I can tell you that if you find an established electrical contractor that has been around your area for a good while and has good references the price will be fair. Most of these guys do not have the biggest add in the Yellow Pages.

  8. #53
    DIY Junior Member Nita Younger's Avatar
    Join Date
    Sep 2011
    Location
    New Jersey
    Posts
    1

    Default Lighted 3-Ways

    Hello All, I am up late obsessing about what I must have done wrong: I just replaced 7 switches, all lighted. As I finished up I noticed one of the switches wasn't lit & isn't working at all. There are 2 3-ways in that box. All the blacks twisted & wire nutted with pigtails (I'm assuming those are the 'Common'. All the Whites & Gnd's also wire-nutted. I added pigtails to ground the switches. BTW there was nothing wrong with the switch I replaced; I was just replacing them all after the downstairs 3-way shocked - there was a bad nick in the common.

    So here is my diagram:

    With switch #1 & switch #2 down, light is = off
    With #1 up & #2 down, light is = on
    With #1 down and #2 up, light is = off
    With #1 & #2 up, light is = on

    This is a 1974 Bi-Level, at the front door are 2 3-way switches controlling 2 lights - 1 entry & 1 downstairs hall. At the bottom of the stairs are 2 switches (1 3-way) controlling the downstairs hall & a room. At the top of the stairs are 3 switches (1 3-way controlling the Entry) & 2 single poles controlling other lights.
    I assumed the switch was bad & replaced it, no luck. I then rewired in 3 different ways, no luck. My neon tester shows the wires are hot. But I agree with jwelectric in that those other testers scare me to death. At least now I know why - lol.
    Thanks

    Update,
    Fixed now. Found an old simple continuity tester, shut of the circuit breakers, with the clip on the black screw (in switch #2) both travelers were on. Finally dawned on me that the problem wasn't in switch #2 - sure enough a traveler & the common were switched in switch #1.
    Last edited by Nita Younger; 09-05-2011 at 03:51 PM. Reason: solved

  9. #54
    DIY Junior Member mestanton11's Avatar
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    2

    Default Tricky problem

    I am trying to figure out a couple 3-way switches for which the wires are routed peculiarly through conduit buried in concrete. In switchbox 1, I have 6 wires, 2 black, 2 white, blue and red. One black is the hot, the other black and one of the whites go to Light 1. The blue and red are travelers. The old switch was wired so Light 1 black was wired onto the post with the blue traveler.
    The second switch (I have no idea of the route the wires took to arrive there) contains the blue, red, white, another mysterious hot black and another black and white to Light 2.
    Maybe something like this:
    ___W____________________________________
    l l
    O [S2]======R/blue==i=[S1]---Hot
    L1 __B___l l l
    B l lW
    O L2
    O is light, B is black, W is white.
    S1 had black wire to light pigtailed to blue traveler wire.
    S2 had blue wire jumped to black light wire. I figured out the juice could travel to both lights that way. Unfortunately, if switch 1 is flipped to blue, light 1 is always on. I must be missing something. It did work correctly before I took it apart. There are 2 circuits in switchbox 2 which I separated. There is also in that box an extra white wire. I don't know which one belongs to which circuit. Sorry for lame picture.
    Thanks for any help or references.
    Picture is screwed up by posting. Sorry. Basically light 1 is wired through switch 1 and light 2 is wired through switch 2.
    Last edited by mestanton11; 12-29-2011 at 07:43 PM.

  10. #55
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    In order for a three way switch to work it must be wired correctly.

    Each switch will have one screw that is marked with the word “common”. Sometimes this screw will be darker color than the other brass looking screws
    The common screw will ALWAYS have either the supply (hot) or the switch leg (the wire going to the light). The common of one switch gets the supply while the common of the other switch gets the switch leg.

    The other two screws are travelers between the two switches. There should never be anything connected to these screws but the travelers which goes from one switch to the other. They do not get pigtails of any kind nor are they wired to any other wire.

    The neutral is always connected so it is not switched. I like to teach that the neutral goes straight to the load with wire nuts.

    There is no way to wire two lights to a set of three way switches where one light is connected to one switch and the other light is connected to the other switch.

    I beg your forgiveness but I can’t make heads or tails out of this.
    ___W____________________________________
    l l
    O [S2]======R/blue==i=[S1]---Hot
    L1 __B___l l l
    B l lW
    O L2

    When you figured that you could light the second fixture by jumping the hot to a traveler you also figured out that this just won’t work the way you want it to work.

    The two conductors going to the two fixtures (switch legs) will need to be connected together in order for the two switches to turn them both on and off at the same time. There is no way to control both lights by jumping from the common to the travelers.
    Last edited by jwelectric; 12-30-2011 at 03:43 AM.

  11. #56
    DIY Junior Member mestanton11's Avatar
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    2

    Default

    Well, that's where I got stuck. I've wired quite a number of 3-way switches in my time, but this one is a poser. It did work, before I took it apart. Thanks for responding.

  12. #57
    DIY Junior Member rgrovier's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1

    Default Going crazy!

    Going crazy ... Appreciate any comments or advice anyone can provide. Here's my situation:

    Had: 2 sets of 3-way switches on 1 breaker as follows:
    Set 1: Stairs - Dimmer at bottom, Rocker switch at top. Installed Lutron Maestro Dimmer/Companion set. No problem.
    Set 2: Hall - Dimmer by bedroom, Rocker switch by stairs. Tried to install Lutron Maestro Dimmer/Companion set. Can't for the life of me get it to work. Even exchanged with the set installed in Set 1. No change - the run that worked continued to work (therefore not the switches). Tried to go back to 3-way Rocker switches at both ends thinking I would "dumb it down" and then go from there. Can't get them to work.

    Here is where I'm at with the Rocker switches: Diagrammed the up/down results as follows:

    Starting with Both Down, lights are OFF.
    Change Switch 2 to UP, lights ON.
    Change Switch 1 to UP, lights remain ON.
    Change Switch 2 to Down, lights remain ON.
    Change Switch 1 to Down, lights turn OFF.

    In a second test:
    Starting with Both UP, lights are ON.
    Change Switch 2 to Down, lights are ON
    Change Switch 1 to Down, lights turn OFF.
    Change Switch 2 to UP, lights are ON.

    In a third test:
    Starting with Both UP, lights are ON.
    Change Switch 1 to Down, lights are ON
    Change Switch 2 to Down, lights turn OFF.
    Change Switch 1 to UP, lights are ON.

    This is the way it looks using the schematic first posted in this thread:
    Down/Down - Off
    Up/Down - On
    Up/Up - On
    Down/Up - On

  13. #58
    DIY Junior Member Kevin S.'s Avatar
    Join Date
    Jan 2012
    Location
    Pennsylvania
    Posts
    1

    Default Troubleshooting two 3-way switch setups

    Quote Originally Posted by Thatguy View Post
    This assumes two travelers between the switches.

    Assign each switch a number.
    With switch #1 & switch #2 down, light is on or off?
    With #1 up & #2 down, light is on or off?
    With #1 down and #2 up, light is on or off?
    With #1 & #2 up, light is on or off?

    In principle, with the answers filled in, the problem(s) can be pinpointed.

    Test cases welcome. . .
    Here's my situation. Any thoughts?

    Off
    On
    Off
    On

    Thanks!

  14. #59
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,645

    Default

    Quote Originally Posted by Kevin S. View Post
    Here's my situation. Any thoughts?

    Off
    On
    Off
    On

    Thanks!

    Short Between the headsets ???
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  15. #60
    DIY Junior Member firecap04@gmail.com's Avatar
    Join Date
    Jan 2012
    Location
    Toledo
    Posts
    3

    Default

    I have an issue...probably overlooking something easy.

    i replaced 4 lights controlled by 2 three way switches. The issue is that one switch does nothing at all. The other works fine.
    Could it be as simple as a bad switch or can I have wires crossed?

    Thanks!

Similar Threads

  1. Troubleshooting our well. Help appreciated
    By Dfrank in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 01-16-2012, 05:41 PM
  2. Furnace Troubleshooting Help
    By mdr in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 01-24-2010, 11:54 AM
  3. Takagi Jr Troubleshooting
    By duff in forum Tankless Water Heater Forum
    Replies: 6
    Last Post: 01-15-2010, 08:44 PM
  4. PRV troubleshooting...
    By Runs with bison in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-03-2009, 01:16 PM
  5. Troubleshooting
    By davewest in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 03-24-2009, 11:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •