Thread: Troubleshooting two 3-way switch setups

  1. #61
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by firecap04@gmail.com View Post
    I have an issue...probably overlooking something easy.

    i replaced 4 lights controlled by 2 three way switches. The issue is that one switch does nothing at all. The other works fine.
    Could it be as simple as a bad switch or can I have wires crossed?

    Thanks!
    or can I have wires crossed

  2. #62
    DIY Junior Member firecap04@gmail.com's Avatar
    Join Date
    Jan 2012
    Location
    Toledo
    Posts
    3

    Default

    That's helpful. Thanks

  3. #63
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by jwelectric View Post
    In order for a three way switch to work it must be wired correctly.

    Each switch will have one screw that is marked with the word “common”. Sometimes this screw will be darker color than the other brass looking screws
    The common screw will ALWAYS have either the supply (hot) or the switch leg (the wire going to the light). The common of one switch gets the supply while the common of the other switch gets the switch leg.

    The other two screws are travelers between the two switches. There should never be anything connected to these screws but the travelers which goes from one switch to the other. They do not get pigtails of any kind nor are they wired to any other wire.

    The neutral is always connected so it is not switched. I like to teach that the neutral goes straight to the load with wire nuts.
    how about this

  4. #64
    DIY Junior Member firecap04@gmail.com's Avatar
    Join Date
    Jan 2012
    Location
    Toledo
    Posts
    3

    Default

    That explains it for me. Thank you

  5. #65
    DIY Junior Member MeasureTwiceCutOnce's Avatar
    Join Date
    Feb 2012
    Location
    Florida
    Posts
    1

    Default

    (IGNORE THIS POST: Problem apparently gone) This one seems a mystery. Went to one of my empty rental properties where I was unaware of any previous problem, and noticed some lights not working. Tenant had turned one breaker off. I turned it on and that breaker controlled two 3 way switches in different rooms that control parallel lights on back patio. There's also a pigtail on what may be the feed (didn't test yet) which likely goes to a single pole in the same room as one of the two 3-ways (or perhaps a receptacle also). Problem is, with breaker on, patio lights stay on all the time no matter what combination is made with the switches (i.e., on, on, on, on). Had to turn breaker back off and haven't gone back to diagnose yet (travelers SEEM to be wired OK at quick glance), but is there an obvious solution here??? UPDATE: For no apparent reason, everything is now working properly. Tenant must have come back to do something, but it wasn't obvious. Anybody ever seeing an on/on/on/on condition is still welcome to reply.
    Last edited by MeasureTwiceCutOnce; 02-02-2012 at 04:18 PM. Reason: Problem disappeared

  6. #66
    DIY Junior Member Amy Broderick's Avatar
    Join Date
    Jul 2012
    Location
    Utah
    Posts
    2

    Default

    Quote Originally Posted by Thatguy View Post
    This assumes two travelers between the switches.

    Assign each switch a number.
    With switch #1 & switch #2 down, light is on or off?
    With #1 up & #2 down, light is on or off?
    With #1 down and #2 up, light is on or off?
    With #1 & #2 up, light is on or off?

    In principle, with the answers filled in, the problem(s) can be pinpointed.

    Test cases welcome. . .
    Off
    On
    On
    On

    Please help!

  7. #67
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    331

    Default

    You have a common and a traveller miswired somewhere in the circuit. Do you know where the power comes to the circuit first? At the light or one of the switches?

  8. #68
    DIY Junior Member Amy Broderick's Avatar
    Join Date
    Jul 2012
    Location
    Utah
    Posts
    2

    Default

    Thanks for the reply ActionDave! The power comes to switch #1 first.

  9. #69
    DIY Junior Member jal's Avatar
    Join Date
    Aug 2012
    Location
    NY
    Posts
    2

    Default

    Here is mine
    off
    off
    off
    on

    Switch 1 regular 3-way has the incoming hot wire - tested with a NCV detector
    Switch 2 is a dimmer with 3-way
    Tested the travelers with an ohm-meter - they are good

    Before this replacement
    Switch 2 was a dimmer where it only had two screws and a traveler and the common were connected to the same screw
    Switch 1 was a regular 3-way
    and the behavior was
    off
    on
    on
    on

    what is going on?
    thanks
    JAL

  10. #70
    DIY Junior Member jal's Avatar
    Join Date
    Aug 2012
    Location
    NY
    Posts
    2

    Default

    Continuing with the above : I put the old 3 way switch and a new 3 way switch (no dimmer)
    I get
    off
    on
    on
    on

    just more info any help appreciated
    JAL

  11. #71
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by jal View Post
    just more info any help appreciated
    JAL
    Anything other than this and the switch will not work

    Quote Originally Posted by jwelectric View Post
    In order for a three way switch to work it must be wired correctly.

    Each switch will have one screw that is marked with the word “common”. Sometimes this screw will be darker color than the other brass looking screws
    The common screw will ALWAYS have either the supply (hot) or the switch leg (the wire going to the light). The common of one switch gets the supply while the common of the other switch gets the switch leg.

    The other two screws are travelers between the two switches. There should never be anything connected to these screws but the travelers which goes from one switch to the other. They do not get pigtails of any kind nor are they wired to any other wire.

    The neutral is always connected so it is not switched. I like to teach that the neutral goes straight to the load with wire nut
    .

Similar Threads

  1. Troubleshooting our well. Help appreciated
    By Dfrank in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 01-16-2012, 05:41 PM
  2. Furnace Troubleshooting Help
    By mdr in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 01-24-2010, 11:54 AM
  3. Takagi Jr Troubleshooting
    By duff in forum Tankless Water Heater Forum
    Replies: 6
    Last Post: 01-15-2010, 08:44 PM
  4. PRV troubleshooting...
    By Runs with bison in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-03-2009, 01:16 PM
  5. Troubleshooting
    By davewest in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 03-24-2009, 11:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •