    I found it is much easier to predict the results given the schematic instead of the other way around, but I can't resist a good puzzle.
    Quote Originally Posted by mgabbard View Post
    #1 down, #2 down - lights are on
    #1 up, #2 down - lights are on
    Taking only the case shown above, if you step through on a piece of paper all 3 ways of hooking up the 3 terminals of a working #1 switch to 3 wires and with switch #1 in both positions [6 diagrams in all] I don't see how this outcome is possible unless you have #22 wiring with 3 travelers.

    An "impossible outcome" means that we are assuming something that is not true.
    What's good about these is that we will probably learn something new. Plus, nobody else wants these budget-busters.

    To find out what it is I'd say check #1 switch with an ohmmeter. If it checks good something has changed inside the walls and that's a separate troubleshooting procedure involving a voltmeter and incand. bulbs.

    There are many different wiring diagrams for this, but I can only find two schematics. In any case it's a source in series with a load in series with an SPST switch made up of two 3-way and zero or more 4-way switches.
    Last edited by Thatguy; 11-23-2010 at 04:48 PM.

  2. #32
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    How would something have changed within the walls? All the wiring should be in accessible junction boxes. If the box was buried there would be no way to make a change to it.

    The example posted is the way that 3 ways work. There is nothing to troubleshoot.

  3. #33
    DIY Junior Member roncarter's Avatar
    Join Date
    Jul 2011
    Location
    Camby Indiana
    Posts
    3

    Default

    Quote Originally Posted by Thatguy View Post
    This assumes two travelers between the switches.

    Assign each switch a number.
    With switch #1 & switch #2 down, light is on or off?
    With #1 up & #2 down, light is on or off?
    With #1 down and #2 up, light is on or off?
    With #1 & #2 up, light is on or off?

    In principle, with the answers filled in, the problem(s) can be pinpointed.

    Test cases welcome. . .
    1 dn 2 dn = off
    1 up 2 dn = off
    1 dn 2 up = on
    1 up 2 up = on

    I replaced porceline sockets (working properly) with can lights and found that I MUST have made an error, and now I seem to be missing the nuetral for 4 of the new lights. If I hook up a jumper wire from the nuetral at sw#1(where feed comes from) the 4 lights work but trips the breaker in one of the variations of switch configurations as follows:

    1 dn 2 dn = off
    1 up 2 dn = trip
    1 dn 2 up = on
    1 up 2 up = trip

  4. #34
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    Switch 3 is probably, but not necessarily, the miswired one, and there are several ways it could be miswired. One problem is that you would have to test switches 1 and 2 under ALL possible configurations to ensure that 3 is actually the misfit.
    Licensed residential and commercial plumber

  5. #35
    DIY Junior Member roncarter's Avatar
    Join Date
    Jul 2011
    Location
    Camby Indiana
    Posts
    3

    Default 3 way switch troubles

    I now have all 3 switches working so they can turn the lights all off and on, BUT... the bulbs (all same wattage) are dim. and if I remove any bulb, the rest of the lamps go off.

  6. #36
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Ron,

    That will save you electricity, being wired in series.

    Nice Job.


    Have a Great evening.


    DonL
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  7. #37
    DIY Junior Member roncarter's Avatar
    Join Date
    Jul 2011
    Location
    Camby Indiana
    Posts
    3

    Default

    Thanks DonL, but they aren't wired in series. At least not in what might be considered the "normal" series circuit.

    It seems that one or more of them are 'hung' on travelers, rather than the neutral and hots. I have 4 boxes to go check to see where I hooked up wrong! All of the boxes are attached to the original ceiling joists 14" above the new 5/8FC ceiling, which obviously makes it very difficult to get to for troubleshooting purposes. I posted here to pick ya'lls brains about where I might start looking to possibly save some aggravation.

  8. #38
    DIY Junior Member Sinestro's Avatar
    Join Date
    Aug 2011
    Location
    Va
    Posts
    5

    Default

    Assign each switch a number.
    With switch #1 & switch #2 down, light is on or off?
    With #1 up & #2 down, light is on or off?
    With #1 down and #2 up, light is on or off?
    With #1 & #2 up, light is on or off?

    off
    on
    on
    on

    The weird thing is, if the downstairs switch is on, then the upstairs switch can't turn off. Both on and off keep the light on.

    This one has been baffling a friend and I for weeks. Any help would be appreciated.

  9. #39
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    It would be my bet that the upstairs switch is not functional due to miswiring, bad switch or it just plain never worked.

  10. #40
    DIY Junior Member Sinestro's Avatar
    Join Date
    Aug 2011
    Location
    Va
    Posts
    5

    Default

    Quote Originally Posted by ActionDave View Post
    It would be my bet that the upstairs switch is not functional due to miswiring, bad switch or it just plain never worked.
    The downstairs switch does the same thing though. Turn on the upstairs switch and you can't turn it off downstairs.

    This all worked until we took down a wall and one of the other light switches

  11. #41
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    My very first electrical wiring was with two 3-way switches. I think I was around 10 or 11 at the time. My father couldn't figure it out and hired an electrician to help. Unfortunately the electrician couldn't figure it out either and while they were gone to buy more fuses, I took up the challenge.

    It was so simple that I could not believe two grown men could not figure it out. I just followed the schematic on the side of the box the switch came in. Also, not having any more fuses, I just screwed a lighbulb into the fuse panel to test. Since it was in series, it was dim but had I got the wiring wrong, rather than blow a fuse, the bulb would be bright.

    When my father and the electrician returned with the fuses, they thought I was pretty bright too.

  12. #42
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by Sinestro View Post
    The downstairs switch does the same thing though. Turn on the upstairs switch and you can't turn it off downstairs.

    This all worked until we took down a wall and one of the other light switches
    Alright then. You have a miswired switch. Nothing more than a WAG but I bet the power came to the light first and after the remodel work a wire was crossed.

  13. #43
    DIY Junior Member Sinestro's Avatar
    Join Date
    Aug 2011
    Location
    Va
    Posts
    5

    Default

    Quote Originally Posted by ActionDave View Post
    Alright then. You have a miswired switch. Nothing more than a WAG but I bet the power came to the light first and after the remodel work a wire was crossed.
    Apologies as I am a bit of a Luddite, but what is a WAG?
    Also, I have read on here that you guys use a "light bulb test". What does that entail?

  14. #44
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Sinestro View Post
    Also, I have read on here that you guys use a "light bulb test". What does that entail?
    Anyone who answers this question will have their post deleted.

    Light bulb testers are death in a socket and unsafe advice will be deleted.

  15. #45
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    WAG = Wild A** Guess

Similar Threads

  1. Troubleshooting our well. Help appreciated
    By Dfrank in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 01-16-2012, 05:41 PM
  2. Furnace Troubleshooting Help
    By mdr in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 01-24-2010, 11:54 AM
  3. Takagi Jr Troubleshooting
    By duff in forum Tankless Water Heater Forum
    Replies: 6
    Last Post: 01-15-2010, 08:44 PM
  4. PRV troubleshooting...
    By Runs with bison in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-03-2009, 01:16 PM
  5. Troubleshooting
    By davewest in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 03-24-2009, 11:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •