Thread: Single receptacle to a double receptacle

  1. #1

    Default Single receptacle to a double receptacle

    I have a single receptacle in my garage that is used for my sprinkler system. I would like to change it to a double to plug in my garage fridge as well. Is this ok to do? When I did it I noticed only one of each wire (black,white, green) coming out of the wall. Should I use a GFCI? Will this cause any problems?? Thanks

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Yes, it should be a GFI.
    How old is the fridge?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3

    Default

    Its an old fridge. Dont really know how old it is. But it will be ok to do with a GFI?

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Maybe not, but the GFI is required and a good idea.

    Old fridges are power HOGS! You are better off biting the bullet and getting a new one. It will pay for itself in a few years for sure.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    Depending on how old the house is, that recepticle might already be controlled (protected) by a GFCI somewhere else. If so, it is supposed to have a sticker on it, but people often neglect to do that or they come off.

    If it isn't already protected, then you should add one, then use the load connections on it to power the second recepticle...no need to buy two as long as the one you do buy has load connections. The incoming power goes to the line connections.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    In the Trades jnaas2's Avatar
    Join Date
    Mar 2009
    Location
    Evansville In
    Posts
    76

    Default

    receptacle circuits in garages dont need gfi if they are not readly accessible or single receptacles that in your case only serve a icebox thats not easily moved to plug something else in according to the 2005 nec code book now if you add a double receptacle and make it so its easy to plug a extension cord in or anything else then it MUST be GFI protected
    Last edited by jnaas2; 05-01-2009 at 06:21 PM.

  7. #7
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    You can check if it is already GFCI protected by running a small incand. lamp from the short outlet slot to a ground. You can use
    http://images.lowes.com/product/conv...64481000md.jpg

    If the fridge doesn't have a grounded plug you should add one in case there's current leakage to the case of the fridge. You'd need to run the ground wire to the metal fridge housing, under a screw. Be sure to scrape the paint so you get a good electrical connection.

    Otherwise the fridge could be or become a shock hazard.

    If you plug in the new grounded plug and it trips a breaker the fridge is already a shock hazard.