    I have two washing machine drains to plumb and vent. I am upgrading them to the proper size 2" using wyes into a short 4" horizontal C.I. section. I can go straight up with a vent. The two washer drains are seperated by a block wall in the basement, as this is a 2 family house. Can I use 1-1/2 for the vents, go straight up and join the two together in the common wall above? From there it would join with a common vent for one of the bathrooms upstairs. A tub and a sink....then up thru the roof and increased to 2"....The existing washer drains had no vents and are 1-1/2" and are poorly done in galvanized pipe.
    Last edited by Rich B; 04-25-2009 at 04:32 PM.

  2. #2
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    I believe what you have planned will work fine, but a real plumber will have more insight as to codes.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default vents

    One thing about the common wall between units, is that it may be considered a fire wall and, if so, any penetrations should be made and sealed with fire resistant materials.

  4. #4
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Under my codes, once you connect the two vents together you'll need to be at 2" for the vents.

    What is your location or what codes are you under?
    A sketch or picture would likely help further.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  5. #5
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Which code is that?

  6. #6
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by nhmaster View Post
    Which code is that?
    Florida Plumbing Code 2007, based on IPC.
    Common, wet and/or waste stack 1-1/2" Vent is only good for 1 dfu.

    Also under FPC the min vent for 1 clothes washer is 2".
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  7. #7
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Me thinks you have mis-interpreted the IPC. You can wet vent an entire bath group off an 1 1/2 pipe.

  8. #8
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by nhmaster View Post
    Me thinks you have mis-interpreted the IPC. You can wet vent an entire bath group off an 1 1/2 pipe.
    I may have. I only have the FPC, the foreward in the FPC indicates its basis on IPC.
    FPC2007 Table 909.3
    Wet Vent/DFU=
    1-1/2"/1 dfu
    2"/4 dfu
    2-1/2"/6 dfu
    3"/12 dfu
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  9. #9
    DIY Member techinstructor's Avatar
    Join Date
    Apr 2009
    Location
    North Carolina
    Posts
    81

    Default

    Quote Originally Posted by FloridaOrange View Post
    I may have. I only have the FPC, the foreward in the FPC indicates its basis on IPC.
    FPC2007 Table 909.3
    Wet Vent/DFU=
    1-1/2"/1 dfu
    2"/4 dfu
    2-1/2"/6 dfu
    3"/12 dfu
    North Carolina code is similar to FL.
    Table: 908.3
    1/1/2"/1 dfu
    2"/4 dfu
    2 1/2" to 3"/6 dfu