Thread: Vent setup ok?

  1. #1

    Default Vent setup ok?

    I'm wondering if someone can look at this diagram I made looking at the plumbing in my house from the bathroom side. Basically it is a 5x 8 bath and you are looking at the 8 foot wall, the toilet connects to the 4 inch stack, followed by a sink in the middle and the bathtub all the way to the right. I'm wondering if the bathtub is adequately vented or if it needs additional PVC attached to it to connect to the 2" vertical vent.

    The 2"x2"x1.5" piece shown would have the 1.5" piece coming out of the side(not down as the diagram shows, as good as I could do for a non isometric drawing).

    Thanks.
    Attached Images Attached Images  

  2. #2
    DIY Member Marty53's Avatar
    Join Date
    Apr 2009
    Location
    New York
    Posts
    44

    Default ...

    I believe it depends on the length of the 1.5" bathtub drain run (<5ft?), and also the length of the 2" run to the main stack vent. Do you have a partition wall behind the tub that you can run a vent up?

  3. #3

    Default

    The 1.5" run from tub drain is approx 3 ft , and the 2" pipe is 2-3 feet to the main stack vent. There is a partition wall behind the tub, but not much room to run the vent up, although if needed I'll have to find a way.

    I am under UPC code also if that will make a difference.

  4. #4
    DIY Member Marty53's Avatar
    Join Date
    Apr 2009
    Location
    New York
    Posts
    44

    Default

    I'd wait for the big boys to chime in, but I'm pretty sure you'll need a vent for that tub.

  5. #5
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Does that tub drain actually run up hill to the lav drain?
    What angle is the wye entering the lav drain at?

  6. #6

    Default

    No, does not run uphill, just a poor drawing. It has a 1/4" per foot decline from the tub to the wye, and the wye is on an angle, 45 degrees maybe. The drawing shows the wye coming out the bottom, but in reality it is coming out of your screen, on an angle if that makes sense.

  7. #7
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Can't have any part of the vent run horizontal until it is 6" above the flood level rim of the highest fixture (the lave in this case) That 2" vent is probably a no go. Tub/shower needs to be within 6' (developed length)of a vent also.

  8. #8
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by nhmaster View Post
    Can't have any part of the vent run horizontal until it is 6" above the flood level rim of the highest fixture (the lave in this case) That 2" vent is probably a no go. Tub/shower needs to be within 6' (developed length)of a vent also.
    I read it as the 2" coming of the lavatory waste line was to the tub. That tub would then be vented off of the lav as long as it's within 8' on a 2" line. Is this not acceptable under UPC? Looks fine for Florida and possibly IPC.
    Last edited by FloridaOrange; 04-22-2009 at 01:18 PM.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  9. #9

    Default

    I'm not sure I totally understand FloridaOrange's view.

    I guess the only way I see that it would vent, if at all, is where the 1.5" pvc tub drain connects to the 2" x 2" x 1.5" wye, and it would have to go up the 2" elbow and into that 2" vent. This would put it under the drain of the sink however.

    Would it be acceptable to put a 1.5" T in the tub drain, come up with one 90 degree elbow, travel closer to the vent pipe, add another 90 degree elbow to come vertical, and then connect into the 2" vent with a 2" x 2" x 1.5" Tee? If it is acceptable how far away from the P trap do I have to put that 1.5" Tee?

    Does the 4" main stack have any venting properties or does that not count?
    Last edited by newowner09; 04-22-2009 at 02:27 PM.

  10. #10
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by newowner09 View Post
    I'm not sure I totally understand FloridaOrange's view.
    If the sink was vented properly the tub would be considered vented at the connection to the horizontal from the sink. Standard stuff down here.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida