I understand that there are a myriad of ways to wire up three way switches, but that's about as far as my knowledge goes. Here's my issue. I've got three cans which are currently controlled by two 3-way switches. I want to add two more switches to control this same set of lights. Access is fairly good in that the walls are open to all but one light and one switch. What is involved in adding these 4-way switches? I'll draw up a diagram if necessary. Thanks.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
switches

There is only ONE way to wire three way switches, and there are a limited, not myriad, number of ways the switches can be physically positioned. The 4-way switches are attached to the two traveler wires between the 3-way switches, AND you have to check the wiring diagram for the switches you use to determine HOW the wires attach to it, i.e. line 1/A and line 2/B.
 

Cej22

Member
Messages
36
Reaction score
0
Points
6
Location
SLC, UT

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
There is only ONE way to wire three way switches

Come on now plumber. You know he meant 3 way circuits.:rolleyes:

The first thing to understand is how your system is wired. You will need to take the switches out and do some simple testing. Details depend on how it's wired.

The next thing to understand is how the 4ways work, along with the 3 ways.

The 3 way circuit uses two traveler wires, sending power on to one or the other of them. The 4way switch simply flips the traveler connections.

You 3way/4way system will have a 3way sw on each end and as many 4ways as you desire in between.

Pull out the switches and see what you have in there. A diagram will be necessary, or at least an accurate written description.



EDIT: IF you existing circuit is not wired thru the lights, all you really need is access to the three wire cable running between the switches. If you can cut that cable and splice onto it, you are good.

Cut the cable and, in a jbox, splice on to a new 3 wire cable and run it to the first 4way, Run the 3 wire cable to the next 4 way, Run the 3 wire cable back to other end of where you cut the cable.

The exact make up of the wiring depends on what colors the original installer used.
 
Last edited by a moderator:

Cej22

Member
Messages
36
Reaction score
0
Points
6
Location
SLC, UT
I think this is starting to make sense. The existing circuit is not wired through the lights.

Here's what I've got. At the top of the stairs is the first switch. 14/3 leads from there to the second switch. There isn't another set of wires in the first box. The second 3-way switch has the common wire from the 14/3 attached, and then the other screws are occupied with the hot and neutral coming from the fixtures. The red wire from the 14/3 goes into a wire nut with hot wires that come from the power source and go to the next switch on the circuit. That's the part that doesn't really match the various diagrams I have. I would have expected the red to go to the second 3-way switch.

If I understand you correctly, it sounds like I can leave the existing three way switches in their current locations by removing the end of the 14/3 from the bottom of the stairs (it's long enough that a junction box wouldn't be necessary) and run it to my 4-ways, then eventually end back up at the 3-way at the bottom of the stairs.
 
Last edited:

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
The second 3-way switch has the common wire from the 14/3 attached, and then the other screws are occupied with the hot and neutral coming from the fixtures.

You are not describing it correctly.

1. The neutral wires are not involved in the switching.

The red wire from the 14/3 goes into a wire nut with hot wires that come from the power source and go to the next switch on the circuit

Here is how a 3way circuit is wired.

The common terminal on one 3W sw is wired to a hot wire (constant 120v)

The common terminal of the other switch is wired to the switch leg (wire going to the light)

There are two wires that connect the other two terminals of both switches (travelers)

It sounds like they used the red to send the power upstairs to the first switch and black and white as travelers.

The black wire going to the fixtures is connected to the common on the bottom of the stairs.

There shoud be two whites connected together in the upstairs box (source neutral and lights neutral.


it sounds like I can leave the existing three way switches in their current locations by removing the end of the 14/3 from the bottom of the stairs

Correct. pull it out and drop in to one 4way location, then the next, then back to the downstairs 3W.

IF the upstairs switch has the RED on the common, wirenut the reds together in the 4way boxes and use the black/whites as travelers.

When you install the 4way switches, I don't remember if they go side to side or tops/bottoms on the switch (it will have 4 terminals. Look at the diagram on the box.
 
Last edited by a moderator:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
I always like to see a diagram in print, rather than folllow text instructions. Google will bring you such diagrams, and the little green book titled "wiring simplified" is a terrific tool for anyone doing electrical work. Available at all the hardware stores.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
semantics

Yes. If you understand the mechanics of a 4 way switch installation, then you can project it to any "configuration", because you will realize that once you interupt the travelers between the two switches, at most you just need two wires to the four way(s), and two wires back, and you can run them anyway you wish to.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
at most you just need two wires to the four way(s), and two wires back, and you can run them anyway you wish to.

While this statement is true, it's not a good idea to deviate from standard wiring methods. The smart thing is to take the 3 wire thru the 4 ways even though you don't actually need the hot leg in switch boxes.
 

Cej22

Member
Messages
36
Reaction score
0
Points
6
Location
SLC, UT
Thanks, guys. I do have the Wiring Simplified book that was recommended, but I'll sheepishly admit that I'm still trying to fully understand 3 and 4-way switches. That's probably plenty obvious.

Sounds like I'm okay in this situation because I can add the 4-ways and hook up the new 14/3 back at the last switch exactly as it's currently configured. I'll figure it out. Thanks for the help.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
I'm still trying to fully understand 3 and 4-way switches.

It's all about understanding the mechanics of the switch. The 3W simply connects the common pole to one or the other of the other two.

The 4way flips them. If you have blk/wht in and blk/wht out, the 4way either connects BB/WW or BW/BW

I saw one really slick animation which showed the current flow as the switches were operated. I have no idea where it was though.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
4way

Just don't do like one person wanted to do. He had installed a 3/14 w/grd from the 3 ways to the 4 way. When I told him he needed four wires to make the 4 way work he wanted to know if the bare ground would work as the fourth wire.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
3-way switches and 4-way switches act like a single SPST switch in series with a source in series with a load, but where all these things are located makes for a lot of combinations.
 

Cej22

Member
Messages
36
Reaction score
0
Points
6
Location
SLC, UT
I'm back again

I can't believe it has been this long since I originally posted about this. Anyway, I was able to get this originally figured out simply by cutting the 14/3 that lead from the upstairs switch to the downstairs switch. I ran it to the first 4-way location and two more subsequent 4-way locations, then back to the downstairs 3-way switch and hooked it up exactly as it was by the electricians during the original build. I'll admit that I did this because I could never really make sense of the original configuration of the 3-way switch, but everything worked just fine when I did it. I simply wired all of the like colors together at the 4-way locations and everything worked great.

Now I'm doing the finish electrical and have run into problems installing the 4-way switches. When I installed the first 4-way switch, I wired the white wires together, and then used the black and reds on the four screws. The lights remained on whether the switch was in the on or off position. They only turned off when the rocker was held in the middle position. I moved the black and red wires top to bottom and side to side, but never got the switch working correctly. So now I'm trying to understand the 3-way switch locations to see how to correct this.

The upstairs 3-way switch is easy. That box has just one 14/3 going into it, with the black wire being attached to the common screw. But the bottom 3-way switch box is quite confusing to me. There are four separate sets of wires in the box for this circuit. I've taken a pic so you can see what I'm dealing with. Three of the whites are wired together. Two of the blacks are wired with the red, and the other two blacks are wired to the 3-way switch. The last white is wired to the switch.

Can anyone make sense of this in very clear terms? What is wrong?

I'll also add that I don't think I'm completely stupid when it comes to this stuff. I added a new circuit with 12 cans on it that has both 3 and 4-way switches. That one works just fine. I just can't make sense of the old work.
 

Attachments

  • DSCF0323.jpg
    DSCF0323.jpg
    42.4 KB · Views: 5,269
Last edited:

ActionDave

Electrician
Messages
418
Reaction score
9
Points
18
Location
Colorado
Red wire is tied in w/ two blacks. Where do the two blacks go? Power in and out perhaps?
 
Last edited:

Jim Port

Electrical Contractor
Messages
156
Reaction score
0
Points
0
Location
Maryland
Website
www.manta.com
The wire pairs on the 4w should be the same colors as the wires on the 2 brass colored terminals on the 3 way switches.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
wires

You cannot just "connect the four wires to the four screws". Two screws are for the wires in, and two are for the wires out, but you have to look at the switch diagram to see which pairs of wires go where. You can connect the wires coming in to either of the two "in" screws and the same with the out one, but you cannot connect one incoming wire to an "in" screw and the other to an "out" terminal. You have mixed yours and therefore the only time it works is at the middle when all the contacts are connected together for an instant.
 

Cej22

Member
Messages
36
Reaction score
0
Points
6
Location
SLC, UT
The wire pairs on the 4w should be the same colors as the wires on the 2 brass colored terminals on the 3 way switches.

So I should wire the reds together at the 4-way locations and use the white ones on the screws instead?. I don't know why the red wire at the 3-way in the picture isn't wired to the switch? Should the wiring be corrected at the 3-way, or does that configuration make sense to you guys. It seems unorthodox from what I've read.
 
Last edited:

Cej22

Member
Messages
36
Reaction score
0
Points
6
Location
SLC, UT
You cannot just "connect the four wires to the four screws". Two screws are for the wires in, and two are for the wires out, but you have to look at the switch diagram to see which pairs of wires go where. You can connect the wires coming in to either of the two "in" screws and the same with the out one, but you cannot connect one incoming wire to an "in" screw and the other to an "out" terminal. You have mixed yours and therefore the only time it works is at the middle when all the contacts are connected together for an instant.

I did connect the same set of wires to the in screws, and then the other set to the out screws. It didn't work. That's when I swapped their locations and tried that. Still no luck.
 