The requirement to bond the gas line is not a NEC requirement but a manufacturer requirement and then only if there is some sort of flexible gas line being used.
If there is a flexible gas line somewhere in the gas piping system then the bonding jumper can land anywhere out lined below;
…shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used.
There is no need to open the panel at all.
Install one of
these sized for two #6 conductors on the #6 running to the ground rod and the other end to the gas pipe with
water pipe clamp. The water pipe clamp must be on solid pipe.
clcik on the blue underlined words