    Default Moen Single Handle Shower/Tub valve problem

    I installed this valve on a friends tub/shower in her basement.

    http://www.moen.com/shared/pdf/82910pt.pdf

    when we turn the hot water on, it comes out the spout just fine.
    if we turn some cold on with it, some water comes out of the shower.
    should we bug moen, about getting a replacement cartridge? or would that help?
    thanks in advance for any advice...

    here's a pic of the install...
    Attached Images Attached Images  
    Last edited by short.circuit; 04-14-2009 at 12:19 AM.

  2. #2
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    No because it was piped incorrectly.
    Read carefully the instructions and you will see that you cannot run PEX to the tub spout.
    The slightly smaller size ID of the PEX creates just enough back pressure to cause water to rise up to the showerhead...

    Only copper or IPS pipe may be used here.

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Apparently you missed the step in the installation instructions where it said to use ONLY copper pipe, NOT pex or cpvc, for the spout drop.

  4. #4

    Default

    fortunately it was a fiberglass, shower/tub surround. was able to remove the 1/2" male & dropear 90. i'm wondering if the pex pipe would work ok with sharkbite fittings. pex fittings look more restrictive. i was tempted, but went with copper & it works fine now. way more flow/pressure.
    lesson learned... thx again

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    You'd have had the same problem with PEX...the ID is smaller than copper.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default shower

    HOW you connected the PEX would not have made any difference. The problem was the PEX itself.