  1. #1

    Default Anyone an electrician or know a good electrical forum?

    Recently had the house rewired. Had an early morning wake-up call from the Pacific Gas and Electric SWAT team today saying that I'm sending current down their gas line!

    They came in and saw that the house has been grounded to the gas pipe from the street just before it goes into the meter. This also connects to a new ground rod I had to have installed. I also have a connection on the main water pipe again with a ground rod. Need 2 grounds to keep San Francisco inspectors happy.

    The PG&E guy told me I have to move the ground connection to the other side of the meter so it is on the pipe coming out of the meter feeding the house rather than on the main feed going into the meter. They say the meter acts as a breaker so this is fine for them (i.e. won't be sending anything down the gas main).

    This all leads me to ask several questions

    How the heck did PG&E know I had a ground on the pipe (what were their sensors picking up?)
    The meter acts as a breaker? Really? How would that work?
    If the meter does really act as a breaker then surely that would defeat the point of me attaching ground to the gas pipe coming out of the meter (i.e. it wouldn’t be grounded?!).

    Strange morning. Does anyone have a clue about this stuff or can point me in the right direction?

    Thanks!!!

  2. #2

    Default

    If I were you, I would call the electrician who performed the work or their company, and the inspection dept that came out and inspected the work and passed it. And tell them what the PG&E told you, and let them deal with it. The electrician and the inspector should know what is required of them. Keeping in mind I am not an electrician just what I would do.

    I would also, repost this in the Electrical forum right here, we got the best electrical guys you will ever find, right here.

  3. #3
    Plumber krow's Avatar
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    906

    Default

    Quote Originally Posted by garnell22 View Post
    If the meter does really act as a breaker then surely that would defeat the point of me attaching ground to the gas pipe coming out of the meter (i.e. it wouldn’t be grounded?!).

    Strange morning. Does anyone have a clue about this stuff or can point me in the right direction?

    Thanks!!!
    The meter or gas pipe does not act as the ground. What they are suggesting is, the gas pipe needs to be grounded on a water pipe or your main water coming in. The gas meter will act as a place for the current coming from an electrical system in your home to stop rather than continuing through your gas main.. In the event of a short circuit in your electrical systems, you do not want to carry the current to the gas mains. (that could run the risk to potentially blow up your neigbourhood)

  4. #4

    Default

    The gas and water pipes must be bonded to the neutral/ground at your electrical service.

    The ground rods connect there also. They allegedly give the lightning somewhere to go.

    The gas piping must be bonded on YOUR side of the meter, I have never seen a gas meter that was not conductive across it. Maybe they use some kind of insulated couplings on theirs.

    If your neutral/ground wire failed between the pole and your service, voltage could be sent down the gas and water lines.
    Last edited by 220/221; 04-02-2009 at 10:55 PM.