    I have a few questions about running a 240 v 60 amp service for a Hot Tub.
    My service panel is located in the basement and the Hot Tub will be on my deck attached to the house. The run in the basement is 30 ft, to where I go thru to the outside under my deck then another 15 ft to the tub. My plan was to run 6/3 ROMEX® from my panel to a weather-tite "J" box then use #6 THHN (4 wires 2 hot, 1 neutral, 1 ground) in PVC conduit to a weather-tite SPA panel with a 60 amp GFCI located within 7 feet of the Hot Tub, then the use liquidtight, flexible nonmetallic conduit to the Hot Tub.
    My concern is: Do I need to have an insulated ground from the Hot Tub back to my main panel in the basement or just to the SPA panel that is located 7 ft from the Hot Tub? If so then I would need to use THHN in conduit all the way.

    Also if I can use 6/3 ROMEX® in the basement, the bear ground in 6/3 ROMEX® is only 12 AWG. Will this be an issue with proper grounding?

    Thanks
    Bob
    Last edited by Terry; 12-07-2011 at 10:24 AM.

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    You must use conduit and individual conductors for the outside portion of the wiring. This part must have an insulated ground. You can come into the back of the weatherproof box with the NM cable where you change over to PVC conduit.

    The inside portion can be NM cable and the bare #10 ground is fine.

    Keep in mind you can only have 6' of flexible. Use some rigid PVC to get closer to the tub then change over to sealtite.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3
    DIY Junior Member bobpat's Avatar
    Join Date
    Mar 2009
    Location
    Western New York
    Posts
    3

    Default

    Thank you very much for the help.
    Bob

  4. #4
    DIY Junior Member bobpat's Avatar
    Join Date
    Mar 2009
    Location
    Western New York
    Posts
    3

    Default

    When I mount the disconnect for the hot tub, what is the recommended height?

    thanks
    bob

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    If you are under the 2008 code cycle and the circuit is protected with a 60 amp overcurrent device then #6 will not pass, the NM will need to be #4.

  6. #6
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    Quote Originally Posted by jwelectric View Post
    If you are under the 2008 code cycle and the circuit is protected with a 60 amp overcurrent device then #6 will not pass, the NM will need to be #4.
    Why is that?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.