    Default What size pipe can I put through a 2x4

    I am finishing my basement. I put in an inside wall for a bar with a sink. I need to run my drain pipe through the wall. Can I run a 2" drain pipe through a two by four?

    Thanks for any help,

    Pat McCurdy

  2. #2
    DIY Member King3244's Avatar
    Join Date
    Dec 2004
    Location
    Kelowna, BC
    Posts
    83

    Default

    The od of a 2 inch plastic pipe is 2 3/8 inches, you will need at least a 2 1/2 inch hole which leaves you with 1/2 inch on either side (obviously). Just make sure that you have nail guards in place so that you don't end up with a drywall nail through your pipe.

    King

  3. #3
    DIY Senior Member Taylor's Avatar
    Join Date
    Mar 2005
    Location
    Northern Joisey
    Posts
    143

  4. #4
    DIY Junior Member
    Join Date
    Jul 2005
    Location
    Fort Collins
    Posts
    2

    Default Appears to not be possible

    Looking at the guidelines it appears it is not possible to put a 2" drain into a 2x4 wall. Is there another way to do this? Could I put steel plates on either side of the wall to support the pipe and then have less greater the 60% bore?

  5. #5
    DIY Member jrejre's Avatar
    Join Date
    Dec 2004
    Location
    Minnesota
    Posts
    61

    Default

    Why do you think that it is not allowed? The link has Figure 3 showing exactly what you are talking about. The note on Figure 3 says:

    "60% allowed in any non-bearing wall or in bearing walls with not more than two successive studs bored and doubled."

    Your situation is more complicated than that??

  6. #6
    General Contractor dx's Avatar
    Join Date
    Jul 2005
    Location
    Michigan
    Posts
    156

    Default

    Pat,

    Are you trying to go through a vertical 2x4, the horizontal (bottom) 2x4, or both? Keep in mind that in a basement, it's extremely rare and unusual to have a load-bearing stud wall. All your 2x4 is doing is supporting drywall. So, for an oversize hole in a vertical stud, just use appropriate blocking above and below the hole to support and stabilize the stud. For a bottom 2x4, it is sufficient to nail the 2x4 to the concrete slab a couple of inches either side of the hole.
    Around here, in new construction, the pipe stub goes in the slab first. Then, the wall is framed around the stub. There is no hole at all in the bottom 2x4, it just stops and starts again on the other side of the pipe. As long as it is properly nailed to the slab, it passes inspection just fine.